    I imagne the inverter he is testing is a 5kw?

  2. #22
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,185
    Thanks
    33
    Thanked 293 Times in 248 Posts
    Quote Originally Posted by Die sparky View Post
    The AC passthrough is 70 amps but can the inverter deliver 70 amps in island mode? Would have to be one hell of a inverter so perhaps 4.6 ohm is correct for the inverter?
    Valid point

    Think we are over thinking

    Dylboy is taking readings in island mode which would mean sizing the output CB of the inverter but we have all been thinking back to incoming CB
    The incoming readings under the incoming CB , being 70Amps, would need to be tested to determine the size for that CB

    Will let Dylboy confirm my thought process .

  3. #23
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,462
    Thanks
    134
    Thanked 694 Times in 592 Posts
    Blog Entries
    1
    A point to remember here. All inverters have a built in Electronic over current detection. Trying to size a CB after the inverter in my opinion is fruitless, as it will trigger long before any circuit breaker will even experience an over current, and in my opinion is merely a circuit isolator more than a circuit breaker.
    In the case that the electronics fails with in the inverter, it in most cases will be a short circuit.
    2 things may happen, either the incoming supply circuit will trip due to the short within the inverter, or the ELU may trip due to their being an earth fault due to the failure.
    In the case that there is a failure in the battery circuit, then the in line battery protection fuse nay blow, alternatively if it is a Lithium then the BMS will disconnect the battery from the battery line.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  4. #24
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,400
    Thanks
    98
    Thanked 139 Times in 132 Posts
    Interesting thread, brothers.

    So basically, it's pointless having a passthrough capability of 70A when the inverter can only deliver say 20A in islanding mode.

    Am I correct in saying that the essential load must be selected so that it should not exceed the islanding mode capability of the inverter ?
    ie. Forget about what the pass through capability is when deciding on the essential load.

  5. #25
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,462
    Thanks
    134
    Thanked 694 Times in 592 Posts
    Blog Entries
    1
    Quote Originally Posted by Derlyn View Post
    Interesting thread, brothers.

    So basically, it's pointless having a passthrough capability of 70A when the inverter can only deliver say 20A in islanding mode.

    Am I correct in saying that the essential load must be selected so that it should not exceed the islanding mode capability of the inverter ?
    ie. Forget about what the pass through capability is when deciding on the essential load.
    I would say yes, as there is a relay in the unit which is probably the rating of the inverter. Exceeding the inverter current would probably trip the inverter even in pass through mode, as I have had my inverter bleeping when power through the inverter starts nearing the inverter capacity
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  6. #26
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,185
    Thanks
    33
    Thanked 293 Times in 248 Posts
    Quote Originally Posted by Derlyn View Post
    Interesting thread, brothers.

    So basically, it's pointless having a passthrough capability of 70A when the inverter can only deliver say 20A in islanding mode.

    Am I correct in saying that the essential load must be selected so that it should not exceed the islanding mode capability of the inverter ?
    ie. Forget about what the pass through capability is when deciding on the essential load.
    Yip - I agree with Justloadit

    Problem is contractors/installers are using bypss current in the design when placing complete houses on inverters and telling owners to switch appliances off and limit load just before loadshedding starts .

    In the real world that is never really successful and they all forget the unknown power outage that happens , besides the fact that regulations do not allow it .

  7. #27
    New Member
    Join Date
    Nov 2023
    Location
    South africa
    Posts
    9
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Justloadit View Post
    A point to remember here. All inverters have a built in Electronic over current detection. Trying to size a CB after the inverter in my opinion is fruitless, as it will trigger long before any circuit breaker will even experience an over current, and in my opinion is merely a circuit isolator more than a circuit breaker.
    In the case that the electronics fails with in the inverter, it in most cases will be a short circuit.
    2 things may happen, either the incoming supply circuit will trip due to the short within the inverter, or the ELU may trip due to their being an earth fault due to the failure.
    In the case that there is a failure in the battery circuit, then the in line battery protection fuse nay blow, alternatively if it is a Lithium then the BMS will disconnect the battery from the battery line.
    Would still be nice to see a circuit breaker and a fuse though.

  8. #28
    New Member
    Join Date
    Nov 2023
    Location
    South africa
    Posts
    9
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Wow pvc conduit bends so much nicer if you dont bend it over the knee. Just grab it like big motorcycle handles and bend it. Also nothing makes my loose my cool more than when the wires to a socket is way too short and when the back box is like 100mm away from the socket😡

  9. #29
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,400
    Thanks
    98
    Thanked 139 Times in 132 Posts
    Quote Originally Posted by GCE View Post
    Yip - I agree with Justloadit

    Problem is contractors/installers are using bypss current in the design when placing complete houses on inverters and telling owners to switch appliances off and limit load just before loadshedding starts .

    In the real world that is never really successful and they all forget the unknown power outage that happens , besides the fact that regulations do not allow it .
    Just a question regarding your statement about regulations not allowing it.

    All I can find is in 7.12.2.4 that states that there must be an automatic disconnecting device should the capacity of the alternate supply be exceeded.
    I take it that the circuit breaker on the output of the inverter will suffice.
    Am I missing something else in the regs ?

  10. #30
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,185
    Thanks
    33
    Thanked 293 Times in 248 Posts
    In my opinion a circuit breaker installed after the inverter/alternative supply is already a given under 16.6.1 for isolation and also under 6.7 , protection

    What I read in this particular reg is that the supply is not overloaded causing a change in voltage or frequency outside of normal.
    That the parts of the installation that may cause an overload are automatically disconnected before any fault/tripping can occur - On bigger installations we use contactors or motorized CB to take out aircons , refrigeration so as not to overload the generator .

    Coming back to a domestic install with an inverter you would need to ensure that either the essential D/Board is sized correctly for the inverter or if you feeding the complete installation that the higher loads are dropped out with a contactor automatically so that you are not relying on homeowner to run around and make sure heaters , dishwashers , geyser , stove etc are switched off before load shedding so as not to overload the inverter.
    If you rely on homeowner to drop the loads , what happens in an unexpected power outage ? it will trip the unit and the chance of voltage dropping out of spec first is high.
    Bear in mind that this reg also stands on 800Kva alternative supplies that could take awhile to trip the CB

    In short - overload protection is a given this is on top of the overload protection.


    7.12.2.4 Where the alternative supply is intended to provide a supply to an
    installation that is not connected to the main supply, or to provide a supply as
    a switched alternative to the main supply, the capacity and operating
    characteristics of the alternative supply shall be such that danger or damage
    to equipment does not arise after the connection or disconnection of any
    intended load as a result of the deviation of the voltage or frequency from the
    standard range. Means shall be provided to automatically disconnect such
    parts of the installation
    , as may be necessary if the capacity of the alternative
    supply is exceeded.

Page 3 of 4 FirstFirst 1234 LastLast

Similar Threads

  1. Zdb / E loop and Psc on sub DB under ELU
    By Dylboy in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 30-Jan-22, 07:09 AM
  2. Inverters
    By ians in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 27-Jan-21, 05:55 PM
  3. Inverters
    By Sparks in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 15-Jul-15, 06:42 AM
  4. Looking for someone who knows about Inverters
    By HR Solutions in forum Local Ads on TFSA
    Replies: 0
    Last Post: 21-Jan-15, 12:55 PM
  5. Inverters
    By HR Solutions in forum General Chat Forum
    Replies: 33
    Last Post: 11-Dec-14, 01:55 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •