Another case, did the E loop and the N loop of a Victron.
E loop of 4.6ohms
N loop of 4.6 ohms.
This means the resistance of the earth wire was the same as the Neautral thus the same readings.
This gives a fault current of 49.3 Amps (the voltage was 227on the rest instrument)
So now that means the output CB needs to be at minimum a 25Amp CB to satisfy the double the current thing as that allows instant trip. (Depending on the type or curve of the breaker).
But the AC passthrough is 70Amps! So putting a 25A main CB basically renders the inverter useless.
So now what happens when it comes to the CoC when we test the inverter supply ?