    Batteries fuse disconnects and the like

    So once again lots of confusion, where do you install busbars, fuses and switch disconnects for batteries for inverters.

    If you have one battery 100 amp/hr, its simple you fit a fuse disconnect with a 125 amp fuse, using a 25 mm fine stranded battery cable designed fot the application.

    If you have you 2 x 100 amp/hr batteires and 1 x inverter: Then you can to connect them in cascade parallel using the same 25 mm cable (because most lithium 100 amp/hr batteries only have 25 mm terminals) connected to a 160 amp fuse disconnect with 125 amp fuses and all is good. Or you could just connect both batteires to a 200 amp fuse disconnect and a 50 mm battery cable from the fuse disconnect to the inverter.

    Now we move onto 3 batteries with 1 inverter, this is where it gets a little more complicated, now you have 3 batteries, some will say it fine you just run a 25 mm cable from each battery to a bussbar, connect the busbar to the inverter using bigger cable 50/70 sqmm. The question some will ask, what protects the cable from the battery to the fuse switch disconnect, the reason you are a fuse is to protect the cables, how do you protect the cable from the battery to the 200 amp fuse? You could once again connect the batteries in cascade parallel (like the cabinet batteires) and take the leads at the end and connect all 4 (2 red and 2 black) to the 200 amp fuse.

    Wall mounting lithium batteires is an expensive installation method, if you plan to fit more than 2.

    Mabye use a Vitctron busbar bar with fuse protection, a 100 amp fuse would protect the battery cable, but what about a double pole disconnect ? Why do you need one.

    To throw a spanner in the works, if the terminals are like sosket outlets and you can just unplug them why the double pole switch disconnect, why not just fuse protection?

    On some batteries the teminals are closed with the a cover which requires a tool to remove the cover to access the terminals.
    Last edited by Isetech; 29-May-23 at 03:44 AM.

  2. #2
    New Member
    Join Date
    May 2023
    Location
    Klerksdorp
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Isetech View Post
    So once again lots of confusion, where do you install busbars, fuses and switch disconnects for batteries for inverters.

    If you have one battery 100 amp/hr, its simple you fit a fuse disconnect with a 125 amp fuse, using a 25 mm fine stranded battery cable designed fot the application.

    If you have you 2 x 100 amp/hr batteires and 1 x inverter: Then you can to connect them in cascade parallel using the same 25 mm cable (because most lithium 100 amp/hr batteries only have 25 mm terminals) connected to a 160 amp fuse disconnect with 125 amp fuses and all is good. Or you could just connect both batteires to a 200 amp fuse disconnect and a 50 mm battery cable from the fuse disconnect to the inverter.

    Now we move onto 3 batteries with 1 inverter, this is where it gets a little more complicated, now you have 3 batteries, some will say it fine you just run a 25 mm cable from each battery to a bussbar, connect the busbar to the inverter using bigger cable 50/70 sqmm. The question some will ask, what protects the cable from the battery to the fuse switch disconnect, the reason you are a fuse is to protect the cables, how do you protect the cable from the battery to the 200 amp fuse? You could once again connect the batteries in cascade parallel (like the cabinet batteires) and take the leads at the end and connect all 4 (2 red and 2 black) to the 200 amp fuse.

    Wall mounting lithium batteires is an expensive installation method, if you plan to fit more than 2.

    Mabye use a Vitctron busbar bar with fuse protection, a 100 amp fuse would protect the battery cable, but what about a double pole disconnect ? Why do you need one.

    To throw a spanner in the works, if the terminals are like sosket outlets and you can just unplug them why the double pole switch disconnect, why not just fuse protection?

    On some batteries the teminals are closed with the a cover which requires a tool to remove the cover to access the terminals.
    Why can't we use 125A DC Double Pole circuit breakers instead of fuses and fuse holders?

  3. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,257
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Quote Originally Posted by Actrox View Post
    Why can't we use 125A DC Double Pole circuit breakers instead of fuses and fuse holders?
    Be careful using DC circuit breakers - the majority are polarized meaning you can only feed through in one direction and they are not suitable for charging and discharging that you have associated with batteries - Read the small print

  4. #4
    New Member
    Join Date
    May 2023
    Location
    Klerksdorp
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by GCE View Post
    Be careful using DC circuit breakers - the majority are polarized meaning you can only feed through in one direction and they are not suitable for charging and discharging that you have associated with batteries - Read the small print
    Yes correct. But if you use bi directional circuit breaker, would that be correct?

  5. #5
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,487
    Thanks
    137
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Quote Originally Posted by Actrox View Post
    Yes correct. But if you use bi directional circuit breaker, would that be correct?
    or connect the breaker in series with the second terminal and the return would be on the same side as entry. This off course would require a 4 pole breaker
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  6. #6
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,050
    Thanks
    55
    Thanked 97 Times in 93 Posts
    I see many people are choosing top leave out the double pole disconnector at each batterry, just fitting abusbar and one fuse disconnect at the inverter.

    The question you need to ask before you do this, does the battery have build in overload protection?

    The cable from the battery is normally only 25/35 sq mm, the fuse a 200 amp fuse with a 50 mm wire from the fuse holder to the inverter, which means beside the double pole isolator, the 25 mm cable is not protected.

    My thought are rather use a Victron power link and fuses for each battery.

    I have noticed Victron dont use double pole battery isolator. disconnects.

  7. #7
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    225
    Thanks
    11
    Thanked 21 Times in 19 Posts
    I have also seen a number of installations with no fuse installed for disconnect since "each battery has a breaker of its own"

    Not sure how safe is it to use those breakers but I believe a disconnect fuse must still be used

Similar Threads

  1. Wire for 125 amp fuse
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 24
    Last Post: 02-Jan-24, 12:32 PM
  2. DC combiner / Fuse / control box
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 24-Apr-23, 03:27 PM
  3. 3 kva inverters and batteries
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 14-Oct-22, 09:12 AM
  4. Guide to fuse replacement
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 04-Jun-16, 11:52 AM
  5. [Question] Rechargeable Batteries - Li-Ion?
    By irneb in forum Technology Forum
    Replies: 8
    Last Post: 27-Nov-08, 08:21 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •