Originally Posted by
Isetech
The way I see it, in a normal domestic installation you should never have the generator connected to he mains while the grid connected. The inverters on the other hand are connected together with the grid and only when in islanding mode will it be disconnected/isolated from the grid.
When you connect a generator, it has mechanical interlocks which can be manually or automatically switched, but should never be connected at any point, hence the break before make contacts.
This is where I believe the confusion arises, when the grid and inverter are operating together, we were taught (right or wrong, that we can discuss another time) that you never bond the neutral/earth after the "point of supply" or at 2 points in an electrical TN-S installations.
While your essential supply (output of the inverter) is connected to the grid, there should never be a bond between neutral and earth.
The only time there should be a bond between neutral and earth is when the inverter is in islanding mode (disconnected from the TN-S system) at which point you create a TN-C before the essential DB, (output from the inverter) , at the essential DB, you would then create a TN-S system and at not point after the DB, should the neutral earth be bonded again.