6.16.7.3 Earth leakage protection shall be provided for the circuit that
supplies an electrode water heater, steam generator or boiler. This protection
shall be set to operate in the event of a leakage current exceeding 10 % of the
current consumed by the appliance under normal conditions of operation. The
characteristics of the circuit and of the earth return path shall be such that the
earth leakage device will operate before the potential between earth and the
shell of the steam generator or boiler exceeds 50 V, including under
short-circuit fault conditions
A formula is required, or must just have normal earthing and bonding like a geyser?