    Separating the DC in a solar system.

    We all know that you cannot run AC and DC and comms cables together, what about battery cables and solar panel cables?

    You battery cables are generally between 12 VDC and 48 VDC and in older solar systems the voltage was around 120 VDC.

    Things have changed, the question is can you fit a DC Distribution board and use it to house all the DC safety gear and fuses?

    Can I fit one DB, fit the fuse protection for the batteries and the solar panel fuses in the same DB?

    Can I run the all the DC cables in the same wireway, if the batteries are 48 VDC and the solar panels are 450 VDC?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,402
    Thanks
    39
    Thanked 331 Times in 278 Posts
    Generally you will not run battery and PV together
    Battery will need a fuse in a holder because of the bidirectional current and DC C/Breakers cant all handle bi directional current
    Pv you need to go into an isolator , fuse and onto DC surge arrestors per string
    Surge arrestor is DC and designed for PV panels

    If you do have them in the same trunking the cables would need to be able to handle the highest voltage

  3. #3
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    776
    Thanks
    121
    Thanked 36 Times in 35 Posts
    So can PV cables be in same trunking, conduit, wireways as AC cables ?

    I see it on almost every single solar installation

    Sent from my CPH2197 using Tapatalk

  4. #4
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    776
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Valsa supplier have a AC and DC protection box... Double tier with both the AC protection and the DC protection... Is that allowed ? They bark on about being SANS what what but then I see this.

    Also seen them use an AC isolator for DC, I asked the sales guy and he just said well they had engineers design and build it....

    Sent from my CPH2197 using Tapatalk

  5. #5
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Quote Originally Posted by GCE View Post
    Generally you will not run battery and PV together
    Battery will need a fuse in a holder because of the bidirectional current and DC C/Breakers cant all handle bi directional current
    Pv you need to go into an isolator , fuse and onto DC surge arrestors per string
    Surge arrestor is DC and designed for PV panels

    If you do have them in the same trunking the cables would need to be able to handle the highest voltage
    Everyone connecting batteries and solar panels, take note of these comments. If you have double insulated solar DC cables which should be rated to 600 or 1000 VDC, makes sure your battery cables are also rated to the string total open VOC.

  6. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,402
    Thanks
    39
    Thanked 331 Times in 278 Posts
    Quote Originally Posted by Dylboy View Post
    So can PV cables be in same trunking, conduit, wireways as AC cables ?

    I see it on almost every single solar installation

    Sent from my CPH2197 using Tapatalk
    No they may not - Unfortunately certain PV installers keep saying there are no regulations governing PV - They seem to miss the point that PV is Electrical installation work as defined and falls directly under SANS10142-1
    Clause 6.1.10 is clear

    6.1.10 Conductors that form part of a d.c. installation shall not be run in the
    same wireway as conductors that form part of an a.c. installation.

  7. Thanks given for this post:

    Dylboy (17-Sep-22)

  8. #7
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,402
    Thanks
    39
    Thanked 331 Times in 278 Posts
    Quote Originally Posted by GCE View Post
    Generally you will not run battery and PV together
    Battery will need a fuse in a holder because of the bidirectional current and DC C/Breakers cant all handle bi directional current
    Pv you need to go into an isolator , fuse and onto DC surge arrestors per string
    Surge arrestor is DC and designed for PV panels

    If you do have them in the same trunking the cables would need to be able to handle the highest voltage
    6.1.7 If conductors that operate at different voltages run in the same wireway,
    the insulation of each conductor shall be able to withstand the highest
    conductor voltage in the wireway. Alternatively, the conductors shall be
    separated by a continuous barrier of insulating material or earthed metal.


    6.3.2.2 Conductors shall be so insulated as to withstand the highest
    temperature and voltage to which they are likely to be exposed.

  9. #8
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    I dont see a problem with using sprag to sleeve the wire to protect the cable /wire, it just cant touch at any point, even at a 90 degree cross.

    The 90 degree crossing of cables/wires has nothing to do with voltages.

    Networks, frequencies and stuff is a completely different topic, in some cases if a VSD is used you would also need to consider cable routes and cross over, shielded cables, etc.

  10. #9
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    776
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Quote Originally Posted by GCE View Post
    No they may not - Unfortunately certain PV installers keep saying there are no regulations governing PV - They seem to miss the point that PV is Electrical installation work as defined and falls directly under SANS10142-1
    Clause 6.1.10 is clear

    6.1.10 Conductors that form part of a d.c. installation shall not be run in the
    same wireway as conductors that form part of an a.c. installation.
    I agree, DC and AC always seperate.

    I do see with these inverters and the layout of the install or nature where it is they have cross over.

    Can DC cut through AC wireway ?
    I say no as it is in the same wireway but I want to make sure.

    I think I have seen one install where AC and DC was seperate everywhere

    Sent from my CPH2197 using Tapatalk

  11. #10
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,274
    Thanks
    60
    Thanked 103 Times in 98 Posts
    Quote Originally Posted by Dylboy View Post
    I agree, DC and AC always seperate.

    I do see with these inverters and the layout of the install or nature where it is they have cross over.

    Can DC cut through AC wireway ?
    I say no as it is in the same wireway but I want to make sure.

    I think I have seen one install where AC and DC was seperate everywhere

    Sent from my CPH2197 using Tapatalk
    My understanding is, so long as you protect the cables from each other. You cant just cut a hole in the trucking and have all the cables touching each other.

    The reality is you never every stop it from happening.

Similar Threads

  1. COC for a solar system
    By ians in forum Electrical Contracting Industry Forum
    Replies: 24
    Last Post: 14-Aug-23, 10:56 AM
  2. [Question] Off grid solar system
    By shaneo in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 02-Jun-21, 09:49 AM
  3. COC REQUIREMENTS FOR SOLAR SYSTEM INSTALLATION
    By Tshepo Mokoena in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 14-Jan-19, 02:23 PM
  4. Solar system installations
    By Siya Saver in forum Energy and Resource Conservation Forum
    Replies: 7
    Last Post: 10-Dec-18, 09:26 AM
  5. solar system and instalation
    By Confidence in forum Electrical Contracting Industry Forum
    Replies: 22
    Last Post: 10-Oct-12, 11:26 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •