    Switch directly eskom vis DB

    HI,

    Advise please.

    I f you install a plug that connects directly to the DB via C/B. Can I use a 4mm wire with C/B 40A and the plug will be 32A. I need to use for portable welding.

    Thanks
    Riyaz

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,247
    Thanks
    34
    Thanked 304 Times in 258 Posts
    4sqmm wire is rated at 32Amps so if you using 40Amp CB then it should be 6sqmm.
    The plug would need to be "welding socket " type rated at 32 Amp and on Earth leakage

  3. #3
    New Member
    Join Date
    Aug 2022
    Location
    SA
    Posts
    4
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Thanks