Thread: Inverter feed

  1. #1
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    776
    Thanks
    121
    Thanked 36 Times in 35 Posts

    Inverter feed

    Hello

    Something not sitting too well with me and would appreciate some guidance please.

    There is an inverter that is fed from the TOP of the Main Switch, the Main Switch is an Earth Leakage.

    Now if you isolate the Main Switch the inverter DB still has power.

    The inverter DB which has a change over and stuff has a main switch for the AC in from the top of the ELU and then a CB for the out put.


    So is it ok that the Main Switch in the DB does not isolate the feed to the inverter rather the inverter DB does that isolation.

    The feed from the TOP of the Earth leakage main switch as it's CB in the inverter DB which is its main switch (double pole)

    Basically is It ok that the main DB main switch does not isolate the feed to the inverter DB ?

    Sent from my CPH2197 using Tapatalk

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,646
    Thanks
    122
    Thanked 155 Times in 146 Posts
    Nope. It's not ok. The main switch of the installation MUST isolate the WHOLE installation.

    How many times have I found this where a second dwelling ( granny flat ) has been built and then the bright spark takes the supply to the granny flat from the top of the main breaker.

    I refuse to issue a coc where I find the above.

  3. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,377
    Thanks
    38
    Thanked 325 Times in 273 Posts
    Not allowed
    Main switch must be the main switch , everything will need to be switched off - The Local main/sub main for the inverter is still needed .

    It would be similar to taking the stove point from the top of the ELU and then saying that the stove has an isolator which is the main switch - I did say similar

  4. #4
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    776
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Brilliant thanks all!

    I do agree. I always have it so that the main switch does all but this one I saw is not like that and not chuffed haha.

    Have not seen it to often so when I saw if Bells went off and searched Sans a bit on site and didn't pick up a quick obvious. Will try find the Reg and then tell the client and motivate to get it changed.



    Sent from my CPH2197 using Tapatalk

  5. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,377
    Thanks
    38
    Thanked 325 Times in 273 Posts
    Here are 2 clauses that should sort any argument


    5.3.7 Disconnecting devices
    An installation shall have disconnecting devices that allow the installation to
    be disconnected for maintenance, testing, fault detection or repair. In the case
    of circuits or items of equipment, additional disconnecting devices could be
    required to allow disconnection for maintenance, testing, fault detection or
    repair of such circuits or equipment.

    6.6.1.1 Each distribution board shall be controlled by a switch-disconnector
    (see 6.9.4). The switch-disconnector shall:
    a) be mounted in the distribution board or adjacent to the distribution board in
    the same room,
    b) in the case of the main or first distribution board of an installation, be
    labelled as "main switch",
    c) in the case of a sub-distribution board, be labelled as "sub-main switch" "or
    main switch" if the board is labelled "sub-board…",
    d) in the case where an alternative supply is installed (emergency supply,
    uninterruptible power systems (UPS), etc.), be labelled as required in
    7.12.2.1, and
    e) have a danger notice on or near it. The danger notice shall give instructions
    that the switch-disconnector be switched off in the event of inadvertent
    contact or leakage.

  6. Thanks given for this post:

    Dylboy (11-Aug-22)

  7. #6
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    776
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Ahhh yes that is true ! Will use those.

    Also found the below: and as far as I know the installation is the Main DB and not the Kiosk at the wall for the property either.

    6.9.1.1 Each installation shall have one disconnecting device to disconnect
    the entire installation, except in the case of multisupplies or more than one
    transformer supplying the installation where each supply shall have its own
    disconnecting device. There shall be a notice fixed next to each such
    disconnecting device indicating that the installation has more than one main
    switch-disconnector.


    Sent from my CPH2197 using Tapatalk

  8. #7
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    776
    Thanks
    121
    Thanked 36 Times in 35 Posts
    What are your thoughts on this then.. same House hahaha.

    The little CB is a 15Amo and does the gate motor...

    This is not controlled via main switch in the DB...

    So it's wrong but now to get a feed there from the DB is major major work.

    Sent from my CPH2197 using Tapatalk
    Attachment 8600

  9. #8
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,646
    Thanks
    122
    Thanked 155 Times in 146 Posts
    Quote Originally Posted by Dylboy View Post
    What are your thoughts on this then.. same House hahaha.

    The little CB is a 15Amo and does the gate motor...

    This is not controlled via main switch in the DB...

    So it's wrong but now to get a feed there from the DB is major major work.

    Sent from my CPH2197 using Tapatalk
    Attachment 8600
    Remove the AC supply from gate motor.
    Install a small solar panel to keep the gate battery charged.

    I have done a couple of gate installations that are far from the house.
    40 or 60A/h lead acid battery, solar panel ............ sorted.

  10. #9
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    776
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Ah good idea ! Funny thing is it is not even 10 meters away the DB hahaha.

    The solar is a good one, a secure complex as well so does not need tobe like farm safe solar haha

    Sent from my CPH2197 using Tapatalk

  11. #10
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    776
    Thanks
    121
    Thanked 36 Times in 35 Posts
    Quote Originally Posted by Derlyn View Post
    Remove the AC supply from gate motor.
    Install a small solar panel to keep the gate battery charged.

    I have done a couple of gate installations that are far from the house.
    40 or 60A/h lead acid battery, solar panel ............ sorted.
    Uncle, what solar charger do you normally use for this setup if I may ask ?

    Sent from my CPH2197 using Tapatalk

Page 1 of 3 123 LastLast

Similar Threads

  1. Pastel Bank feed setup
    By HJVW in forum Accounting Forum
    Replies: 1
    Last Post: 23-Nov-20, 12:11 PM
  2. Twitter RSS feed
    By sterne.law@gmail.com in forum Technology Forum
    Replies: 5
    Last Post: 26-Aug-13, 10:02 PM
  3. 10 reasons why GM won't feed the world
    By duncan drennan in forum General Chat Forum
    Replies: 3
    Last Post: 06-May-08, 10:51 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •