    Bathroom extraction fan.

    Hi all
    I have had a look at some previous comments on this topic but it is still not clear to me.

    1. Can a bathroom extraction fan be connected from the bathroom light live and neutral to the extraction fan isolator or plug to the extraction fan.

    2.Can the extraction fan isolator or plug be in the ceiling not in the bathroom.

    3.Can the extraction fan be installed in the ceiling above the shower cubicle.Where can it be positioned.

    Thanks

    Sent from my MAR-LX1A using Tapatalk

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,246
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    Clause 6.16.4.3 allows you to use an isolator or 5 amp socket from a light circuit and as long as the fan is outside of Zone 3 it is allowed



    6.16.4.3 Extraction fans
    Where an extraction fan supply is switched with a luminaire, it shall be
    connected to the switched portion of the light circuit, provided that the fan
    circuit is connected by means of a SANS 164-3 or SANS 164-2-1 or
    SANS 164-2-2 socket-outlet or a switch disconnector.

    7.1.1.3 Electrical equipment, including appliances (although appliances are
    not covered by this part of SANS 10142), shall not be installed in a bathroom
    except under the conditions given in table 7.1. No electrical equipment shall
    be installed in zone 0 except in accordance with 7.1.3.2. (see also 7.1.4.4).

    7.1.2.4 Zone 3
    Zone 3 is limited by
    a) the vertical plane external to zone 2 and the parallel vertical plane 2,40 m
    external to zone 2, and
    b) the floor and the horizontal plane 2,25 m above the floor.


  3. #3
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    Thanks
    If zone 1s vertical height is 2,5m. Does that mean anything higher is outside of the zones so I could mount the extractor fan in this area on the ceiling.

    Sent from my MAR-LX1A using Tapatalk

  4. #4
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    Quote Originally Posted by Gtfast View Post
    Thanks
    If zone 1s vertical height is 2,5m. Does that mean anything higher is outside of the zones so I could mount the extractor fan in this area on the ceiling.

    Sent from my MAR-LX1A using Tapatalk
    Or just use IPX5 extractor fan.

    Sent from my MAR-LX1A using Tapatalk

  5. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,246
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Quote Originally Posted by Gtfast View Post
    Thanks
    If zone 1s vertical height is 2,5m. Does that mean anything higher is outside of the zones so I could mount the extractor fan in this area on the ceiling.

    Sent from my MAR-LX1A using Tapatalk
    You should be safe to do so

  6. Thanks given for this post:

    Gtfast (13-Jul-22)

  7. #6
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    Hi all
    Looking at the regs again.
    Concerning installing ceiling extractor fan in shower area..
    Table 7.1 indicates fixed appliances in Zone 2 should be installed as per A and B1 or B2.
    It makes no mention of Degrees of protection.
    Reg 7.1.4.1 indicates in Zone 2 the equipment should have protection of IPX4.
    In Zone 2 do we have to apply table 7.1 and reg 7.1.4.1.
    The extractor fan must be IPX4 rated and be connected as per A and B1 or B2.
    Some input would be appreciated.
    Thanks

    Sent from my CPH2197 using Tapatalk

  8. #7
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,246
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Quote Originally Posted by Gtfast View Post
    Hi all
    Looking at the regs again.
    Concerning installing ceiling extractor fan in shower area..
    Table 7.1 indicates fixed appliances in Zone 2 should be installed as per A and B1 or B2.
    It makes no mention of Degrees of protection.
    Reg 7.1.4.1 indicates in Zone 2 the equipment should have protection of IPX4.
    In Zone 2 do we have to apply table 7.1 and reg 7.1.4.1.
    The extractor fan must be IPX4 rated and be connected as per A and B1 or B2.
    Some input would be appreciated.
    Thanks

    Sent from my CPH2197 using Tapatalk
    The zone is determined by the dimensions around a bath or shower - Do not get confuse with the actual room the shower happens to be in.

    read the zoning dimensions in conjunction with Fig 7.1.3



    7.1.2.3 Zone 2
    Zone 2 is limited by
    a) the volume external to zone 1 and the parallel vertical plane 0,60 m
    external to zone 1, and
    b) the floor and the horizontal plane 2,25 m above the flo

  9. Thanks given for this post:

    Gtfast (10-Nov-22)

  10. #8
    Full Member
    Join Date
    Apr 2016
    Location
    South Africa
    Posts
    75
    Thanks
    34
    Thanked 1 Time in 1 Post
    Thanks maby were missing one another.

    I have noticed something in the field.

    Refering to table 7.1 and reg 7.1.4.1

    In zone 2 would one place an extractor fan that has
    IPX4 protection be on earth leakage and not able to touch with standard test finger.
    Or
    IPX4 protection and be a class 2 appliance

    Is the IPX4 necessary which is not on table 7.1.

    It seems that they are saying you can connect as per table 7.1 only ,but then there is reg 7.1.4.1.

    Table 7.1 — Conditions under which electrical equipment may be
    installed in a bathroom

    7.1.4 Selection and erection of electrical equipment
    7.1.4.1 Degrees of protection
    Electrical equipment shall have at least the following degrees of
    protection against ingress of water:
    in zone 0: IPX7;
    b) in zone 1: IPX5;
    c) in zone 2: IPX4;
    d) in zone 3: IP21; and
    e) outside zone 3 in the same room: IP21, except for a distribution board
    Thanks


    Sent from my CPH2197 using Tapatalk

  11. #9
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,246
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Written clause takes preference - Most illustrations are informative

  12. Thanks given for this post:

    Gtfast (11-Nov-22)

Similar Threads

  1. 230VAC socket in bathroom
    By mygoggie in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 14-Jan-22, 12:17 PM
  2. Sauna in a bathroom
    By ians in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 18-Jul-13, 04:51 PM
  3. [Question] Extraction System
    By AmithS in forum Food Industry Forum
    Replies: 4
    Last Post: 12-Dec-10, 11:37 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •