    V-O-V Generator - doing my head in!

    After brushing up on my 10142 the other day I came across a MacAfric Diesel genset that befuddles the mind - N-E 154V (Yes..read that again!) and L-E 66V. WTF!!

    Client has this connected to his DB.

    I didn't fully understand VOV until today - what is the solution? (Apart from dumping the very expensive diesel gen?)

  2. #2
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    There are a couple of threads on this, hit the search and they should pop up.

    Some options are to disconnect the output earth of the genny and then bridge the the Neautral and the Earth going to the DB. How ever it has to be before the changeover as you can not have the permanent bridge there. Don't just bridge the Neautral and earth of the genny output as the earth is a centre tap. It you do. Ridge the centre tap you may damage the genny and basically short out half the coil.

    Some are to disconnect the earth centre tap in the genny itself too.

    But search the forum and a bunch should pop of for reading and I may have missed some stuff.. been a long day of beer...

    Sent from my CPH2197 using Tapatalk

  3. #3
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Thinking again... Use a contactor rather to make that N E bridge... Doing a perm one even at the change over at the input of the genny would still not have it disconnect when in change over so if the grid as issues it may be the N and E point for the street...

    Sent from my CPH2197 using Tapatalk

  4. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,521
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Regarding the diesel genset, find the live and neutral wires coming from the stator, disconnect them and megger each one down to earth. If open circuit then there is not an internal connection from the main stator to earth. Ie no centre tap earth connection.

    If that is the case, one can quite safely bridge the neutral to earth on the genset. We do that regularly on genny installations.

    It is very important to first ensure that there is no centre tap earth connection before bridging anything otherwise you will be shorting out half the stator and the genny wont survive for any length of time after that.

  5. #5
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,662
    Thanks
    3,307
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    Quote Originally Posted by Dylboy View Post
    Thinking again... Use a contactor rather to make that N E bridge... Doing a perm one even at the change over at the input of the genny would still not have it disconnect when in change over so if the grid as issues it may be the N and E point for the street...

    Sent from my CPH2197 using Tapatalk
    When on mains supply, the neutral from the generator must be disconnected from the installation as well as the live. Therefore the N to E bridge on the generator doesn't become the N to E bridge point "for the street". The generator neutral will remain connected to earth only.

  6. #6
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Quote Originally Posted by Dave A View Post
    When on mains supply, the neutral from the generator must be disconnected from the installation as well as the live. Therefore the N to E bridge on the generator doesn't become the N to E bridge point "for the street". The generator neutral will remain connected to earth only.
    Yes ya, will draw it out but surely the change over would break that Line and Neautral if genny when on Grid thus breaking the N and E of the street ?

    Sent from my CPH2197 using Tapatalk

  7. #7
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,051
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Quote Originally Posted by Dylboy View Post
    Yes ya, will draw it out but surely the change over would break that Line and Neautral if genny when on Grid thus breaking the N and E of the street ?

    Sent from my CPH2197 using Tapatalk
    If you wire it correctly. the neutral earth bond should be done in the changeover DB before the generator input at the changeover switch.

    Just be careful with inverters, its not the same.

  8. #8
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Quote Originally Posted by Isetech View Post
    If you wire it correctly. the neutral earth bond should be done in the changeover DB before the generator input at the changeover switch.

    Just be careful with inverters, its not the same.
    Yes that's where I have it in my mind to do it there

    Ya inverters are different but that is where i use contactors for that.

    I mean you can buy a N E bridge box from Segen but using a contactor is the same.

    But appreciate all the input as always guys. Learning stuff everyday with this forum

    Sent from my CPH2197 using Tapatalk

Similar Threads

  1. Windows head technician
    By ians in forum General Chat Forum
    Replies: 18
    Last Post: 30-Oct-13, 08:47 AM
  2. Bruise from pre-school: Defensive & abusive head
    By Erika Gordon in forum General Chat Forum
    Replies: 14
    Last Post: 17-May-10, 03:31 PM
  3. Zuma 'not right in the head'
    By duncan drennan in forum South African Politics Forum
    Replies: 1
    Last Post: 05-Sep-07, 10:08 AM
  4. New ICASA head
    By duncan drennan in forum Technology Forum
    Replies: 3
    Last Post: 18-Aug-07, 08:54 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •