Thread: Earth leakage trip on switching over inverter to main supply

  1. #1
    Full Member
    Join Date
    Jan 2019
    Location
    Durbanville
    Posts
    38
    Thanks
    43
    Thanked 0 Times in 0 Posts

    Earth leakage trip on switching over inverter to main supply

    I had a case where the we installed an inverter and inverter db that we split the circuits for load shedding purposes, all wiring was previously on the E/L of main DB (Lights also). So upon connecting the new inverter DB we split the light circuit from the E/L and put all the lights on the inverter DB, skipping the E/L, some plugs we did put on E/L, so when running on the inverter everything is fine, when switching over the changeover sw to eskom the main db E/L trips, but inverter E/L stays on, funny thing is the lights is not on the E/L and is connected upstream on a double pole breaker isolator supplying from the main isolator bypassing both the earth leakages in the 2 DB's
    Now i traced the light circuit and found some connections that was connected to a 12V power supply supplying 4x 12Volt downlighters, i isolated these wires and everything now works fine, E/L now working 100%
    How come is this, could it be the 4 x 12 v lights on the power supply, where i normally connect 1 power supply per downlight as per spec.?
    And why did it trip the E/L when it was connected before the E/L?
    I tried looking at older posts but could not find anything similar, anybody to steer me in the right direction...?

  2. #2
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,771
    Thanks
    3,328
    Thanked 2,692 Times in 2,269 Posts
    Blog Entries
    12
    You have to be really careful about getting your neutral onto the correct neutral busbar relative to the live, even though the circuit wasn't on any of the E/L units. Was the live on the load side of the inverter and the neutral connected to a neutral bar on the supply side of the inverter perhaps?

  3. Thanks given for this post:

    Gene (12-Jul-22)

  4. #3
    Full Member
    Join Date
    Jan 2019
    Location
    Durbanville
    Posts
    38
    Thanks
    43
    Thanked 0 Times in 0 Posts
    Thanks for the reply, yes wiring on db is correct as well the Inverter db, only theory i have is that the lighting circuit neutral could be mixed - thus the trip, so just disconnected it in the roof.

Similar Threads

  1. [Question] Earth leakage trip at specific times
    By Silpo in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 29-Dec-21, 01:32 PM
  2. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM
  3. earth leakage trip on 30mA
    By Thys LOW Elektries in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 06-Sep-21, 09:48 PM
  4. [Article] Earth leakage unit problems (trip) after solar installation
    By Dries in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 09-Sep-15, 04:13 PM
  5. earth leakage trip due to lightning
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 19-Dec-14, 07:33 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •