    Quote Originally Posted by Derlyn View Post
    Another question for this morning, gents.

    Busy with a rewire.

    Gate motor has been wired with 1,5mm FTE to the lights circuit.

    If the gate motor has an isolator and that specific breaker is labelled "lights & gate motor", is it legal ?

    Will save on having to lay 2,5mm and wiring to a plug circuit.
    I would say if the CB is max a 15amp then it should be ok for the 1.5mm.

    I have seen that before and deemed it ok and the boss did too. But maybe there is something I am missing with it

    Edit: is a gate motor an appliance ? If so then a mixed circuit is ok

    6.15.4.1 Except as allowed in 6.15.4.2, 6.15.4.3 and 6.16.3.2.3, there shall
    be no mixed loading of circuits.
    6.15.4.2 Except as required in 6.16, a non-dedicated single-phase circuit that
    has overcurrent protection rated at not more than 20 A may supply a mixed
    load of a combination of any socket-outlets rated at not more than 16 A,
    luminaires and fixed appliances.

    Sent from my CPH2197 using Tapatalk
    Last edited by Dylboy; 28-Jun-22 at 10:23 AM.

  2. #12
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,051
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Quote Originally Posted by Derlyn View Post
    Another question for this morning, gents.

    Busy with a rewire.

    Gate motor has been wired with 1,5mm FTE to the lights circuit.

    If the gate motor has an isolator and that specific breaker is labelled "lights & gate motor", is it legal ?

    Will save on having to lay 2,5mm and wiring to a plug circuit.
    Just be careful of the intercom wire in the same conduit as the gate wiring, very common. You cannot run a 12 VDC comms cable in the same pipe as the 1.5 mm twin+E or any other cable.

    Gate installations and regulations are a whole thread on its own.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. The brain drain
    By Derlyn in forum General Chat Forum
    Replies: 0
    Last Post: 19-May-22, 07:32 PM
  2. Brain fart, 3phase
    By Dylboy in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 18-Jan-22, 12:03 PM
  3. brain teaser
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 21-Feb-10, 09:52 PM
  4. MTN - are they all brain dead?
    By Sieg in forum General Business Forum
    Replies: 25
    Last Post: 18-Jul-09, 04:32 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •