    Going back there later in the week.

    What I'm scratching my head about is that on a 2 wire TNCS supply, when doing a line earth impedance test and a neutral impedance test, the readings should be the same as you are testing the same cable. Earth and neutral are common on the same conductor.

    The question is. .... when doing a loop impedance test, is the impedance of the live wire in the loop also measured by the meter and included in the result ?

    I'm thinking that there may be a high impedance on the live conductor somewhere.

  2. #12
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    723
    Thanks
    118
    Thanked 33 Times in 32 Posts
    Yes ya the line wire is included. The way I see it with the TNCS is that the earth where it now becomes earth cable as in seperated is that at the seperation point there is a high resistance.


    In my brain a loop test and Neautral test should just be 2 leads as you are testing 2 cables as such, so having 3 is weird in my brain.

    Having 3 works in my brain if the machine has both the earth loop and the Neautral loop in one push of the button.


    Sent from my CPH2197 using Tapatalk

Page 2 of 2 FirstFirst 12

Similar Threads

  1. [Question] Looking for Caseware experienced junior accountant
    By JO@Ledgr in forum Accounting Forum
    Replies: 1
    Last Post: 09-Jun-21, 12:56 PM
  2. Experienced bookkeeper Alberton
    By Andromeda in forum Local Ads on TFSA
    Replies: 4
    Last Post: 25-Oct-18, 02:11 PM
  3. Looking for Highly Experienced App Developers
    By Random Hero in forum General Business Forum
    Replies: 0
    Last Post: 08-Dec-16, 07:13 AM
  4. Experienced & unemployed
    By JanChris in forum BEE and Employment Equity Forum
    Replies: 35
    Last Post: 08-Jul-14, 06:51 PM
  5. [Opinion] HAVE YOU EXPERIENCED A HOME LOAN LATELY?
    By green door in forum Business Finance Forum
    Replies: 0
    Last Post: 22-Nov-09, 09:53 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •