  1. #21
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    For downlights there is not always an earth terminal depending on what GU10 fitting you use. So then the earthing of the earth terminal is not valid as there is no earth terminal.

    The issues is often with downlights almost always

    Sent from my CPH2197 using Tapatalk

  2. #22
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,505
    Thanks
    106
    Thanked 146 Times in 139 Posts
    If you buy a 220 Volt downlight holder there IS an earthing terminal.

    The one's without an earthing terminal were made for 12V use.

  3. #23
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,505
    Thanks
    106
    Thanked 146 Times in 139 Posts
    If someone says it's out of arm's reach, therefore doesn't need to be earthed ........... just ask them if the geyser in the attic is also out of arm's reach. End of discussion.

  4. #24
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,505
    Thanks
    106
    Thanked 146 Times in 139 Posts
    If someone has a query regarding a coc that has been issued, surely the first port of call would be the electrician who issued same.

    His particulars are on the coc.

  5. #25
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,039
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Quote Originally Posted by Dave A View Post
    It is statements like this that trouble me.

    Was it also pointed out that if there is an earth terminal, it must be connected?
    And who at the ECA would have said such a thing?

    Every time the issue has ever come up at the ECA SA that has crossed my desk, or at a meeting that I have attended, the emphasis has been just what GCE has pointed to - that the "out of arms reach" is not an exemption from the earthing requirements of 6.12.3.1.

    My experience is the drive at the ECA SA is the very opposite of what you have suggested here.
    It also troubles me.

    I call the number on the ECA logo at the top of page 2, the same number the public or anyone enquiring about the COC.

  6. #26
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,039
    Thanks
    55
    Thanked 97 Times in 93 Posts
    What is even more concerning is the false sense of safety, people think having a COC for their property would create a safer environment. With a 100 % fail rate on COC's audits just in my little operation, just imagine how bad it is in reality .

Page 3 of 3 FirstFirst 123

Similar Threads

  1. Size of Earth conductor
    By Andrew_van_Zyl in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 07-Jun-22, 01:36 PM
  2. [Question] Earth Tag as Earth Continuity Conductor
    By Matt.24 in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 07-Oct-21, 09:02 AM
  3. Twin and earth stripped.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 25-May-21, 06:12 PM
  4. Twin and earth connections .
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 23-Feb-18, 08:59 PM
  5. twin and earth question
    By Hotspot in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 20-Jun-16, 10:10 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •