    I updated a DB board and installed new lights in an old building that was wired with VIR (Vulcanized Indian Rubber).

    Insulation at the ends was crumbly and I landed up having to ferrule and extend with new copper conductors in places.

    I meggered the installation afterwards. Interestingly the readings exceeded 1MOhm.

    My question: I know the VIR will deteriorate further and I want to suggest to my client that we remove all VIR and replace with modern cable. But if the installation passes COC tests is it necessary?

    Thoughts?

    Sent from my SM-A226B using Tapatalk

  2. #2
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    398
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by Andrew_van_Zyl View Post
    I updated a DB board and installed new lights in an old building that was wired with VIR (Vulcanized Indian Rubber).

    Insulation at the ends was crumbly and I landed up having to ferrule and extend with new copper conductors in places.

    I meggered the installation afterwards. Interestingly the readings exceeded 1MOhm.

    My question: I know the VIR will deteriorate further and I want to suggest to my client that we remove all VIR and replace with modern cable. But if the installation passes COC tests is it necessary?

    Thoughts?

    Sent from my SM-A226B using Tapatalk
    Somewhere in the regs there is a bit about the cake having to be continuous along its length. I feel that by doing what you have you have changed the characteristics of said cable.
    I personally would not do it that way but whether it is legal or not would depend on your interpretation of the regs.

    Sent from my SM-A528B using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  3. Thanks given for this post:

    Andrew_van_Zyl (02-Jun-22)

  4. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,253
    Thanks
    34
    Thanked 305 Times in 259 Posts
    There have been previous discussions around VIR

    At the time of discussion this was my take on it

    The old wiring you refer to is VIR wiring ( vulcanised India Rubber ) and was used extensively on the cleat system.
    When the wiring was manufactured it had a life span of 25 years - As far as I am aware they stopped manufacturing almost 40 years ago - If you looked through Fundamental requirements note 2 pg 62 in SANS 10142-1 "manufacturers instructions may contain more stringent requirements " - I would say the VIR wiring is not allowed and would not sign a COC


    Here is a link for convivence - https://www.theforumsa.co.za/forums/...read.php/22594

  5. Thanks given for this post:

    Andrew_van_Zyl (02-Jun-22)

  6. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,519
    Thanks
    106
    Thanked 146 Times in 139 Posts
    I have rewired numerous houses, replacing all the VIR with pvc insulated wiring.

    The grey area for me is the section between the roofbox and the municipal meter as that falls outside the scope of the coc.

  7. Thanks given for this post:

    Andrew_van_Zyl (02-Jun-22)

  8. #5
    Bronze Member
    Join Date
    Mar 2022
    Location
    Little Falls, Roodepoort
    Posts
    122
    Thanks
    54
    Thanked 9 Times in 8 Posts
    A mate suggested heat shrinking the stub of cable coming into the DB as far as possible

  9. #6
    Bronze Member
    Join Date
    Mar 2022
    Location
    Little Falls, Roodepoort
    Posts
    122
    Thanks
    54
    Thanked 9 Times in 8 Posts
    What is the going rate in JHB to replace the VIR with PVC, per socket outlet and light fitting? Concrete deck ceiling

Similar Threads

  1. MV and LV Cables in Substation
    By Adriaan.S in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 28-Apr-21, 05:30 AM
  2. Green Powered Buildings & Training?????
    By insulin in forum Energy and Resource Conservation Forum
    Replies: 5
    Last Post: 13-Sep-10, 03:02 PM
  3. Trade and Industry on energy efficiency regulations for new buildings
    By I Robot in forum Electrical Load Shedding Forum
    Replies: 1
    Last Post: 16-Jun-10, 08:50 AM
  4. The changing face of office buildings [article]
    By Debbiedle in forum Business Finance Forum
    Replies: 2
    Last Post: 09-Sep-09, 12:31 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •