    Quote Originally Posted by Dylboy View Post
    I would, I would try Google for specs of the CB to see if any markings in manual as well.

    Also would put a sticker stating line at bottom.

    NB is to make sure ELU is wired correct as they are often line top and load bottom but other than that I think all fine.

    Sent from my CPH2197 using Tapatalk
    So we have a YES

    Your comment about the ELU is interesting, if using a Hybrid inverter, and the power is feeding back in to the non essential DB which is fed via an ELU, would the ELU function correctly ?

  2. #12
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Ahhh interesting on the hybrid backfeeding.... It would not go through the ELU as would go straight to busbar... How ever the ELU does trip when i test but I need to draw this out now hahaha.

    But good point on the now reverse fed now too ok markings...



    Sent from my CPH2197 using Tapatalk

  3. #13
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,521
    Thanks
    106
    Thanked 146 Times in 139 Posts
    The current is changing direction through all the breakers and the earth leakage 50 times a second irrespective of whether the supply is in the top or in the bottom.

    Makes no difference.

    Remember we talking AC. ( alternating current )

  4. #14
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,050
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Quote Originally Posted by Derlyn View Post
    The current is changing direction through all the breakers and the earth leakage 50 times a second irrespective of whether the supply is in the top or in the bottom.

    Makes no difference.

    Remember we talking AC. ( alternating current )

    I am trying to understand why we waste time going in the top and out the bottom of devices which create more resistance (longer wires) waste time and wire.

    So even if you still the busbar on the top of the circuit breaker, you could wire in the top of the mains isolator (which by the way was always installed in the bottom out the top) out the bottom a bridge from the bottom of the isolator to the bottom of the ELU, out the top and connect the busbar directly to the top of the ELU?

  5. #15
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,050
    Thanks
    55
    Thanked 97 Times in 93 Posts
    If you use Onesto products, there is a label which clearly indicates the Line at the top and load at the bottom on the circuit breakers and there is an arrow on the KCN which faces from top to bottom.

    Why can some some breakers operate in both direction and other only in one direction, IE line/load.

  6. #16
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,488
    Thanks
    137
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Quote Originally Posted by Derlyn View Post
    The current is changing direction through all the breakers and the earth leakage 50 times a second irrespective of whether the supply is in the top or in the bottom.

    Makes no difference.

    Remember we talking AC. ( alternating current )
    True, however the mechanical construction of the circuit breaker will dominate the manner in which it is to be connected, such as which terminal with in the breaker will always have power, and how the arc is dispersed?
    lets take a relay, do you connect live to the moving terminal and load to the stationary terminal?
    or do you connect the live to the stationary terminal and the load to the moving terminal?
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  7. #17
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Very interesting and good reminder that it osolates and not flows as we always think flow like DC.



    Sent from my CPH2197 using Tapatalk

  8. #18
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,521
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Quote Originally Posted by Justloadit View Post
    True, however the mechanical construction of the circuit breaker will dominate the manner in which it is to be connected, such as which terminal with in the breaker will always have power, and how the arc is dispersed?
    lets take a relay, do you connect live to the moving terminal and load to the stationary terminal?
    or do you connect the live to the stationary terminal and the load to the moving terminal?
    Just checked all the relays I have in the workshop.
    The moving terminals have no connections to the outside.
    Much like a contactor, the moving connections either make or break the 2 stationary terminals.
    It does not matter which stationary contact is used for line or load.

  9. #19
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,050
    Thanks
    55
    Thanked 97 Times in 93 Posts
    After watching a few circuit breaker videos, something I noticed about the construction of the breaker, which could be the deciding factor, but then how would a non polarised breaker work ?

    A circuit breaker has a short circuit and and overload protection and a few other things to consider, but we not going down that road. Keeping it in simple terms, the overload protection is achieved using a a strip which bends according to temperature and overload protection is achieved by using a coil and sleeve.

    The way I would see how they might select line and load would be by the side the protective devices are installed: ie if the coil and strip is is connected to the bottom terminal then that terminal would be the load, if connected to the top, that terminal would be load.

    Then we have the arc shutter, this could be what determines the line and load?

    I find that in SA we just do as we are told, people make rules and everyone follows blindly. As pointed out in anther thread, one person can influence an entire industry (geyser connected to than ELU) , not that the info could be incorrect, just the fact that there are not enough people with the knowledge to dispute the recommendation. Like the ZA plug rule, how on earth did that regulation even get past the suggestion box? A quick trip to the local appliance store would have cleared up that silly reg. The only time you will see me installing more than 2 ZA sockets in a room, would be at tables in a restaurant. For that application I give it the thumbs up, why because 90 % of the people who go to the Mugg and Bean for example between 08:00 and 14.00 might plug in a laptop or phone, so a standard socket for the laptop and a ZA plug for the phone good idea, and that is it. My kitchen has 14 socket outlets of which 2 are ZA. I will be replacing another socket with one of those 6 x 2 pin in my charge cupboard because I dont need a standard socket in the cupboard, for charging devices only.

  10. #20
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,050
    Thanks
    55
    Thanked 97 Times in 93 Posts
    This video tells it as it is for most of us tradesmen, there are a few exceptions, but I think most of us would agree, when we were stuck in an airconditioned room with some person rattling on about some crap out of a book, scribbling stuff of a whiteboard, most of us, were still trying to recover from the night out. there was a lot nodding I learnt most of what I know today from on site experience and night school many years after I qualified. I got 14 % for N4 mathematics, once I settled done with a family, I went back to classes and got 89 %, it wasnt that I was stupid, I just had no interest in maths and classroom studies.


    This video by the way is a really bad explanation of line and load, I just thought his comment at the beginning was appropriate for us tradesmen. Please feel free to add a video with a decent explanation of why a circuit breaker/device has line and load.


    https://www.youtube.com/watch?v=N3vu...nel=HVACSchool

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Circuit breaker bussbar
    By ians in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 09-Mar-21, 06:36 PM
  2. Circuit breaker compliance
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 24-Jul-20, 12:53 PM
  3. Circuit Breaker faulty?
    By Melchior in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 09-Mar-17, 11:18 PM
  4. Circuit Breaker tester
    By ELECT 1 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 21-Dec-13, 12:17 AM
  5. buzzzing circuit breaker
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 08-Mar-11, 10:47 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •