    6.8.1 Circuit-breakers used as main or local switch-disconnectors
    A circuit-breaker that is used as a main or local switch-disconnector (see 6.9.4) shall comply with the relevant requirements of a standard given in clause 4 for switch-disconnectors, or, alternatively, a switch-disconnector shall be positioned on the supply side of the circuit-breaker.

    Sent from my SM-A528B using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  2. #12
    Junior Member
    Join Date
    Oct 2018
    Location
    Gauteng
    Posts
    19
    Thanks
    2
    Thanked 2 Times in 2 Posts
    Why does he need to add a circuit breaker ? He replaced the old RCCB with a new RCCB ... and the RCCB acts as the local switch disconnector

  3. #13
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    I'm not familiar with the term RCCB. If an RCCB is an earth leakage disconnector with an integrated circuit breaker, then that will suffice.
    If it is an earth leakage disconnector with no integrated circuit breaker, then a circuit breaker must be installed on the load side of the earth leakage disconnector.

    Sent from my SM-A528B using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  4. #14
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    Quote Originally Posted by BobZA View Post
    Why does he need to add a circuit breaker ? He replaced the old RCCB with a new RCCB ... and the RCCB acts as the local switch disconnector
    Yes he needs to add a 63a mcb before the RCD as this unit does not have overload protection if he had installed a RCD with oveload protection then it can be used as a main switch at the moment there is no overoad current protecting the 16mm incoming cable except for the council kiosk.

  5. #15
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    If you want to use Lear as jou have then the unit you need is the one in the picture. I am not very fond of the Lear units they are difficult to reset.
    Click image for larger version. 

Name:	150753-1.jpg 
Views:	98 
Size:	14.0 KB 
ID:	8528

  6. #16
    Junior Member
    Join Date
    Oct 2018
    Location
    Gauteng
    Posts
    19
    Thanks
    2
    Thanked 2 Times in 2 Posts
    Quote Originally Posted by Alfred M View Post
    Yes he needs to add a 63a mcb before the RCD as this unit does not have overload protection if he had installed a RCD with oveload protection then it can be used as a main switch at the moment there is no overload current protecting the 16mm incoming cable except for the council kiosk.
    I am not an expert on the regs but I don't see anywhere that says the main switch needs to provide overload protection. All I see is "6.6.1.1 Each distribution board shall be controlled by a switch-disconnector".

    The incoming cable is protected by the council board. And all the circuits in the DB are protected by individual circuit breakers (after the RCCB).

    My understanding is that the "distribution board switch-disconnector" or "main switch" is for isolation purposes so this function can be fulfilled with the RCCB device. Of course most modern circuit breakers can also be used as switch disconnectors ... but I do not see the requirement for a "distribution board - main overload device"

    Or am I maybe misunderstanding this particular installation?

  7. #17
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Read 6.8.1 together with 6.7.5.7. I think that should make it more clearer

    Sent from my SM-A528B using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  8. #18
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,484
    Thanks
    104
    Thanked 142 Times in 135 Posts
    Each phase conductor of an installation shall have both overload and short circuit protection (6.7.1.1)

    Now check out (6.7.1.3 )
    These conductors may be protected by the suppliers overcurrent protective device, provided that
    A) the supplier agrees
    B)
    C) the user has access to the device.

    The supplier generally will not agree and these devices are usually in a locked kiosk, so the user does not have access to them.

    Here in our valley, the supply authority prefers a circuit breaker as mains in the main db so that should there be a major short or fault on the installation, it trips on the installation instead of outside in the kiosk or on the pole.

    Makes sense.

  9. #19
    Junior Member
    Join Date
    Oct 2018
    Location
    Gauteng
    Posts
    19
    Thanks
    2
    Thanked 2 Times in 2 Posts
    Quote Originally Posted by Leecatt View Post
    Read 6.8.1 together with 6.7.5.7. I think that should make it more clearer

    Sent from my SM-A528B using Tapatalk
    Thanks Leecatt. As usual a long way around in the specs. Could really be simplified. If overload is required on main switch ... then just say it.

    But thanks I see your point ...

  10. #20
    Junior Member
    Join Date
    Oct 2018
    Location
    Gauteng
    Posts
    19
    Thanks
    2
    Thanked 2 Times in 2 Posts
    Quote Originally Posted by Derlyn View Post
    Each phase conductor of an installation shall have both overload and short circuit protection (6.7.1.1)

    Now check out (6.7.1.3 )
    These conductors may be protected by the suppliers overcurrent protective device, provided that
    A) the supplier agrees
    B)
    C) the user has access to the device.

    The supplier generally will not agree and these devices are usually in a locked kiosk, so the user does not have access to them.

    Here in our valley, the supply authority prefers a circuit breaker as mains in the main db so that should there be a major short or fault on the installation, it trips on the installation instead of outside in the kiosk or on the pole.

    Makes sense.
    Thanks Derlyn. What you say makes sense from a practical point off view.

    And I note what Leecat said ... but I have certainly seen some installations where the main switch is only an earth leakage switch without overload. Again makes me think the regs need rework

Page 2 of 3 FirstFirst 123 LastLast

Similar Threads

  1. Home alterations and electrical plans question
    By adrianh in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 02-Oct-20, 11:34 PM
  2. [Question] Installing new electrical outlets in my home
    By julies in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 26-Aug-14, 06:22 AM
  3. Safety at home and work
    By adrianh in forum General Chat Forum
    Replies: 1
    Last Post: 13-May-14, 12:16 PM
  4. safety at home
    By murdock in forum General Chat Forum
    Replies: 5
    Last Post: 16-Jul-10, 08:24 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •