Thread: Neutral/earth bond for inverters

  1. #1
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,047
    Thanks
    55
    Thanked 97 Times in 93 Posts

    Neutral/earth bond for inverters

    If you installed an Axpert type inverter, chances are you have bonded the neutral to earth, between the inverter output terminal and the top of the output earth leakage unit, and you dont have an earth earth leakage on the inverter supply. The debate about supplying the inverter via an earth leakage would be an interesting one.

    I will soon be adding a Sunsynk 5 kva inverter to my workbench, this is were it gets a little complicated. I have been doing some research into this inverter (for about 2 years) because I just dont have the funds to outlay on a Victron unit yet, maybe once I get my Bugatti, all the blue will blend together in the garage.

    It seems people use an external neutral earth bridge connected using a relay. The sunsynk is a hybrid which complicates things a little, capable of receiving and send power back to the grid. There seems to be a lot of confusion about this.

    Anyone has a simple explanation which is easy for everyone to understand.

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,487
    Thanks
    137
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    A statement by someone about Sengen -

    I spoke to the guys from Segen who are also selling the Sunsync now. They said the inverter has a built in earth neutral bond and that bonding is only recommended at one single point and that a permanent bond can cause impedance issues.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. #3
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,487
    Thanks
    137
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Check this video
    Automatic Neutral Earth Bonding

    Do a google search on SunSync videos, lots of training materials.
    I have the Deye which is made in the same factory, can state that I am very happy with it, and it does what the manual says.
    Since installing it, I save about 50% on my electricity bill, but bear in mind, that my 2 geysers geysers is running on my own designed Dual Usedasun Geyser System so is not even part of the savings
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  4. Thanks given for this post:

    Isetech (27-Apr-22)

  5. #4
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,662
    Thanks
    3,307
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    I suspect hybrid inverters have to deal with the neutral-earth bonding issues. My Growatt certainly does too, so add that to the list that "just works". Probably due to the "complexities", as you say.

    I did have a plan as to how to deal with the issue if I had found the neutral was floating at any point (using a relay to drop out the bond when the municipal supply is on), but happily not an issue.

    I have no idea why the supply to the inverter would need to be on earth leakage. Surely what you want protected by earth leakage is what the inverter supplies...

  6. #5
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,519
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Quote Originally Posted by Dave A View Post

    I have no idea why the supply to the inverter would need to be on earth leakage. Surely what you want protected by earth leakage is what the inverter supplies...
    What happens if you use your earth leakage tester on the output of the invertor ?
    Does the earth leakage relay on the input side ( supply) trip ?

  7. #6
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,047
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Quote Originally Posted by Dave A View Post
    I suspect hybrid inverters have to deal with the neutral-earth bonding issues. My Growatt certainly does too, so add that to the list that "just works". Probably due to the "complexities", as you say.

    I did have a plan as to how to deal with the issue if I had found the neutral was floating at any point (using a relay to drop out the bond when the municipal supply is on), but happily not an issue.

    I have no idea why the supply to the inverter would need to be on earth leakage. Surely what you want protected by earth leakage is what the inverter supplies...
    Been watching the Sunsynk training videos, Keith mentions certain countries require RCD protection on the input side of the inverter.

    This external neutral relay sound like a dangerous option, especially if the relay fails or doesnt switch fast enough or too fast, it will result in the supply E/L unit tripping. It could explain why there are so many queries about E/L unit tripping when the power switches to backup then back to power.

    Throw in a hybrid inverter and many different type so electrical system and you have a task trying to find the right solution for that specific application.

    I had to remove the earth/neutral bond to prevent the supply E/L unit from tripping.

  8. #7
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,047
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Quote Originally Posted by Derlyn View Post
    What happens if you use your earth leakage tester on the output of the invertor ?
    Does the earth leakage relay on the input side ( supply) trip ?
    Without the neutral/earth bridge.

    With the mains power on - both earth leakage units trip. The E/L unit in the Workshop DB and the E/L unit on changeover panel.

    With the mains power off - only 2 lights are on the plug tester and the E/L units feeding the essential circuit does not trip.

    If you fit the neutral/earth bridge between the inverter output and the input side of the E/L unit, you cant switch on the workshop E/L unit, until you remove the bridge. If you add a relay with a neutral/earth bridge, it could get rather interesting.

    I have sure there must have been a lot of research into this neutral/earth bridge, we just need to find the documentation.

  9. #8
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,519
    Thanks
    106
    Thanked 146 Times in 139 Posts
    So in other words with mains power off, there is no earth leakage protection on the inverter output circuits.

  10. #9
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,487
    Thanks
    137
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Quote Originally Posted by Derlyn View Post
    So in other words with mains power off, there is no earth leakage protection on the inverter output circuits.
    You use the ELU after the inverter for the loads.
    If there is no Neutral Earth bond when there is a Mains failure, then the Neutral and Live will slowly increase in potential to earth due to high frequency switching inside the inverter. This could rise to a few thousand volts, now if you touch Neutral and Earth, you could get a fatal discharge of this built up static charge. By connecting the Neutral to Earth with a bond, you prevent this static build up from occurring.
    This is the reason that if you do not use the Earth Neutral bond, and the Neutral/Live load has built up a charge, and then gets connected to Mains, the ELU will see the discharge as an Earth fault and trip.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  11. #10
    Full Member
    Join Date
    Aug 2018
    Location
    Capetown
    Posts
    42
    Thanks
    0
    Thanked 1 Time in 1 Post
    Someone connected a sunsynk inverter without the external N-E relay and that caused some alarm and camera power supplies to blow.
    I suspect the output is similar to the vov generators without the neutral to earth bonding. Just my opinion.

    Sent from my R1PLUS_1 using Tapatalk

Page 1 of 11 123 ... LastLast

Similar Threads

  1. High neutral earth reading
    By Thys LOW Elektries in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 27-Mar-22, 02:26 PM
  2. [Question] Poor Neutral/Earth Bond - Stubborn Nuisance Trips
    By Ewaldvdh in forum Electrical Contracting Industry Forum
    Replies: 25
    Last Post: 23-Mar-22, 01:32 PM
  3. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM
  4. Voltage between Neutral and Earth - When is it a fault?
    By Justloadit in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 20-Jul-19, 09:23 PM
  5. Neutral leaking 220V to Earth
    By Etienne Swanepoel in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 19-Oct-14, 07:37 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •