What I did with my Sunsynk/Deye inverter was to ignore the "island" output of the inverter you would normally use to power a relay to do the earth-neutral bond. Instead I installed a
Hager 25A 1NO+1NC contactor in the DB. The contactor will close whenever grid power is lost and bond neutral to earth - and obviously when power restored, the contactor will open and break the bond. No particular reason other than it being neater in my opinion having it in the DB vs having it in the inverter cubby. Another reason I prefer doing it this way: The contactor will open immediately when grid power is restored whereas with the inverter, it will keep the relay powered (and thus the bond) until it synchronizes with the grid. By default configuration that is 60 seconds.
As for my earth leakage. I have two earth leakages. One for the grid, and another for the UPS output of the inverter. Both having their own separate neutral bars. The automatic transfer switches that I use will then switch the relevant circuits to either UPS Live+Neutral or Grid Live+Neutral.