Page 2 of 11 FirstFirst 1234 ... LastLast
Results 11 to 20 of 101

Thread: Neutral/earth bond for inverters

  1. #11
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Yes without it if I recall correctly i would measure 98 volts around there of N to E. So I can see that cussing issues for electronics and also the ELU won't work.

    Sent from my SM-N960F using Tapatalk

  2. #12
    Bronze Member
    Join Date
    Feb 2022
    Location
    South Africa
    Posts
    130
    Thanks
    0
    Thanked 13 Times in 12 Posts
    Quote Originally Posted by Derlyn View Post
    What happens if you use your earth leakage tester on the output of the invertor ?
    Does the earth leakage relay on the input side ( supply) trip ?
    The reason is that all inverters have capacitors to earth from both neutral and live. These are to mitigate EMI/RFI from the switching transients. These capacitors cause current in the earth conductors: transient currents, plus some milliamps of 50 Hz current. Both of these make a Residual Current Device before the inverter more likely to nuisance trip. You can still have them, but not the usual 30 mA ones. But then of course, there is less protection so what is the point

  3. #13
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,041
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Note the reference to class I and class II products.

    Something else the I am still trying to wrap my head around, how I will fit a changeover/bypass switch in this system and as he mentions is not required.

    https://www.youtube.com/watch?v=QtDb...hannel=Sunsynk

  4. #14
    Junior Member
    Join Date
    Nov 2020
    Location
    Cape Town
    Posts
    24
    Thanks
    0
    Thanked 2 Times in 1 Post
    What I did with my Sunsynk/Deye inverter was to ignore the "island" output of the inverter you would normally use to power a relay to do the earth-neutral bond. Instead I installed a Hager 25A 1NO+1NC contactor in the DB. The contactor will close whenever grid power is lost and bond neutral to earth - and obviously when power restored, the contactor will open and break the bond. No particular reason other than it being neater in my opinion having it in the DB vs having it in the inverter cubby. Another reason I prefer doing it this way: The contactor will open immediately when grid power is restored whereas with the inverter, it will keep the relay powered (and thus the bond) until it synchronizes with the grid. By default configuration that is 60 seconds.

    As for my earth leakage. I have two earth leakages. One for the grid, and another for the UPS output of the inverter. Both having their own separate neutral bars. The automatic transfer switches that I use will then switch the relevant circuits to either UPS Live+Neutral or Grid Live+Neutral.

  5. Thank given for this post:

    Cyon (26-May-22), Dave A (26-May-22)

  6. #15
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,041
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Why a neutral/earth bond relay is used in conjunction with RCD's

    https://www.youtube.com/watch?v=mQR5...hannel=Sunsynk

  7. #16
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,041
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Quote Originally Posted by recre8 View Post
    What I did with my Sunsynk/Deye inverter was to ignore the "island" output of the inverter you would normally use to power a relay to do the earth-neutral bond. Instead I installed a Hager 25A 1NO+1NC contactor in the DB. The contactor will close whenever grid power is lost and bond neutral to earth - and obviously when power restored, the contactor will open and break the bond. No particular reason other than it being neater in my opinion having it in the DB vs having it in the inverter cubby. Another reason I prefer doing it this way: The contactor will open immediately when grid power is restored whereas with the inverter, it will keep the relay powered (and thus the bond) until it synchronizes with the grid. By default configuration that is 60 seconds.

    As for my earth leakage. I have two earth leakages. One for the grid, and another for the UPS output of the inverter. Both having their own separate neutral bars. The automatic transfer switches that I use will then switch the relevant circuits to either UPS Live+Neutral or Grid Live+Neutral.
    A smart idea to make it a fail safe way of doing it, if the relay fails, it will trip your grid E/L unit.

  8. #17
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,041
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Quote Originally Posted by recre8 View Post

    As for my earth leakage. I have two earth leakages. One for the grid, and another for the UPS output of the inverter. Both having their own separate neutral bars. The automatic transfer switches that I use will then switch the relevant circuits to either UPS Live+Neutral or Grid Live+Neutral.
    Not sure why you do this ?

    The hybrid inverter is bi directional so the power flows into the inverter and back out the inverter on the grid side. If the inverter goes into islanding mode and power is fed from the batteries, the solar panel could charge the batteries, but not feed back into the grid.

    The only reason I would install a changeover/transfer/ bypass switch would be to feed power to the essential/UPS DB if the inverter had to be isolated from the system for maintenance or repair.

    I am still trying to figue why a person would connect an earth leakage unit/RCB to the supply side of the inverter in SA ?

    I cant wait to get the Sunsynk inverter so that I can start tinkering. I cant seem to find any 1C rated batteries at a reasonable price. Hubble and all their suppliers are out of stock. There is talk that Sunsynk have a 1 C battery being launched soon.

    I would be interested to see your wiring configuration.

  9. #18
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Hey man

    So the bi directional is only when there is excess is solar..

    So there are three ports.
    Grid
    Aux
    Load

    The load is where you connect your essential items.

    Aux can be for genny input or other circuits that you want a small amount on essential but there is then a battery limit to when that circuit can be used. I.e between 60 and 70% then it can be used.

    The grid is there you connect the feed Into from the DB, then when there is excess solar and batteries are full it then feeds back on that circuit to go to your non essential loads but does not back feed as the CT coil is installed as a goal keeper to stop it going past him.

    When island mode is initiated as Eskom is off then the inverter will not feed any excess back on the Grid feed even if there is excess however your Load (essential circuits) will have access to the solar and batteries and also the Aux port.

    Sorry if you knew all this but I am not 100% sure so figured just to type it in case

    Sent from my CPH2197 using Tapatalk

  10. Thanks given for this post:

    Isetech (05-Feb-23)

  11. #19
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,248
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Quote Originally Posted by Dylboy View Post
    Hey man

    So the bi directional is only when there is excess is solar..
    Can the Sunsynk use batteries to feed back into the grid ?

  12. #20
    Junior Member
    Join Date
    Nov 2020
    Location
    Cape Town
    Posts
    24
    Thanks
    0
    Thanked 2 Times in 1 Post
    Quote Originally Posted by Isetech View Post
    Not sure why you do this ?

    The hybrid inverter is bi directional so the power flows into the inverter and back out the inverter on the grid side. If the inverter goes into islanding mode and power is fed from the batteries, the solar panel could charge the batteries, but not feed back into the grid.

    The only reason I would install a changeover/transfer/ bypass switch would be to feed power to the essential/UPS DB if the inverter had to be isolated from the system for maintenance or repair.
    Apologies if you know most of this already.
    It depends on your usage I suppose. In my case, I want to have backup power if the grid goes down. So the transfer switch, switches my loads to the Sunsynk's UPS port. When the grid goes down, the Sunsynk doesn't push any power out of the GRID port so if you want to power anything during an outage, it has to be connected to the UPS port. BUT, this also means that when the grid is on, your loads are essentially being passed through the Sunsynk. And the Sunsynk 5kW I have is only rated for 35A current flowing through it. Given that on certains days where the dishwasher, washing machine and tumble dryer are running... switching on a kettle could exceed this. Hence the transfer switches. The transfer switches just allow me to swap the loads between pulling current through the inverter/having backup power OR pulling current directly from the DB. When the grid is on, and the inverter is feeding power through it's GRID port, the net result is the same.

    Quote Originally Posted by Isetech View Post
    I am still trying to figue why a person would connect an earth leakage unit/RCB to the supply side of the inverter in SA ?
    The GRID port of the inverter should be connected BEFORE the EL/RCD. The UPS port of the inverter should have it's own EL/RCD.

    Quote Originally Posted by Isetech View Post
    I cant wait to get the Sunsynk inverter so that I can start tinkering. I cant seem to find any 1C rated batteries at a reasonable price. Hubble and all their suppliers are out of stock. There is talk that Sunsynk have a 1 C battery being launched soon.

    I would be interested to see your wiring configuration.
    Sure. Attached is the diagram from a year ago when I planned it. Might be a little unclear. DB_Export.pdfHaven't had any issues or nuisance trips whatsoever. I'm not an electrician or certified in anyway so use with caution. I just sent the diagram to a reputable electrician and had him come inspect after I did the job to get a CoC.

    EDIT: PDF attached to post, but it doesn't seem to show. Here is a link.

Page 2 of 11 FirstFirst 1234 ... LastLast

Similar Threads

  1. High neutral earth reading
    By Thys LOW Elektries in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 27-Mar-22, 02:26 PM
  2. [Question] Poor Neutral/Earth Bond - Stubborn Nuisance Trips
    By Ewaldvdh in forum Electrical Contracting Industry Forum
    Replies: 25
    Last Post: 23-Mar-22, 01:32 PM
  3. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM
  4. Voltage between Neutral and Earth - When is it a fault?
    By Justloadit in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 20-Jul-19, 09:23 PM
  5. Neutral leaking 220V to Earth
    By Etienne Swanepoel in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 19-Oct-14, 07:37 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •