Thread: Welding Plug Earth Leakage

  1. #1
    Junior Member
    Join Date
    Oct 2018
    Location
    Gauteng
    Posts
    19
    Thanks
    2
    Thanked 2 Times in 2 Posts

    Welding Plug Earth Leakage

    HI All,

    Looking into power supply to client's 400V 20A 3P+E welding plug. I would appreciate some thoughts on the following:

    It seems clear that according to SANS10142 we do require "earth leakage protection if the circuit is intended to supply portable or stationary class I appliances". What is not clear is the size of the earth leakage. The 30mA requirement seems to cover only the normal 230V 16A sockets ... but what about the Welding Plugs? I know in the past 30mA can cause nuisance trips for Welding Machines etc..

    What do you guys use for Welding Plugs earth leakage units ?

    Thanks In Advance ...

  2. #2
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Hello

    Below states a 30mA, it copied more than what i wanted but phone giving issues.

    7.4.6.5 The metalwork shall be protected against corrosion and the damage
    expected under site conditions. The final finish shall be orange.
    7.4.6.6 Isolating devices shall be suitable for securing in the off position (for
    example, a padlock or location inside a lockable enclosure).
    7.4.6.7 The distribution board shall contain
    a) one or more multi-element robust LED indicator lamps per phase to show
    that the board is alive. HRC fuses or correctly rated circuit-breakers within
    the board shall protect these lamps,
    b) where required, four-pin (three-phase and earth) welding socket-outlets,
    typically 63 A rating, each of which shall be protected by a circuit-breaker
    and 30 mA earth leakage protection,
    c) where required, three-pin (phase neutral and earth) welding socket-outlets
    rated at 32 A with associated circuit-breakers and 30 mA earth leakage
    protection. This shall particularly be provided for portable single-phase
    welding sets, and
    d) switched socket-outlets (16 A), connected in pairs to individual single-pole
    20 A combined circuit-breakers and 30 mA earth leakage protection of
    sufficient number.
    7.4.6.8 The circuit-breakers and associated earth leakage relays referred to

    Sent from my SM-N960F using Tapatalk

  3. Thanks given for this post:

    BobZA (21-Apr-22)

  4. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,257
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Hi BobZA

    The regulations pasted by Dylboy are relevant to construction sites

    Reg 6.7.5 is relevant to your particular question
    6.7.5 deals with single phase and 3 phase socket outlets and stipulates 30mA earth leakage to be used ( pasted below)

    To prevent nuisance tripping use a earth leakage per socket outlet or every 2nd one. We use integrated ELU with overload protection to save space in the D/Boards.

    The majority of time that we have been asked to look into nuisance tripping there have been multiply socket outlets on 1 unit and the accumulation of leakage to earth has been the problem
    Split the circuits and we have solved the issue



    6.7.5.2 Industrial type single-phase and three-phase socket-outlets (including
    "welding" socket-outlets) shall comply with the requirements of SANS 60309-1
    and SANS 60309-2 and, except as allowed in 6.7.5.5 and 7.10.1.6, shall have
    earth leakage protection if the circuit is intended to supply portable or
    stationary class I appliances.

    6.7.5.4 Unless allowed elsewhere in this part of SANS 10142 or for a special
    application, the rated earth leakage tripping current (rated residual current) IΔn
    required to activate an earth leakage protection device shall not exceed
    30 mA.
    It shall not be possible to desensitize an earth leakage protection
    device while the circuit in which it is installed is in service. However, this does
    not prevent the use of non-integral earth leakage protection devices when the
    rupturing capacity exceeds 2,5 kA.

  5. Thanks given for this post:

    BobZA (21-Apr-22)

  6. #4
    Junior Member
    Join Date
    Oct 2018
    Location
    Gauteng
    Posts
    19
    Thanks
    2
    Thanked 2 Times in 2 Posts
    Perfect. Thanks Guys!

  7. #5
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Thanks GCE, didn't properly look sorry and see its chapter 7 even haha.

    Sent from my SM-N960F using Tapatalk

Similar Threads

  1. Replies: 7
    Last Post: 14-Dec-21, 05:23 PM
  2. [Question] new Earth Leakage NOT tripping with plug tester
    By Fredre in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 12-Jun-20, 12:41 PM
  3. Dedicated plug circuits, what is allowed to be supplied by a non earth leakage protected socket?
    By hartdev@hotmail.com in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 19-May-17, 06:52 AM
  4. Earth leakage tripping when plug in snake rack
    By MattyN in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 22-Aug-15, 09:29 AM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •