    Oven below Distribution board

    Hi
    I am starting a renovation of a small apartment kitchen soon and the DB is in a position that makes it difficult. I know I can’t have a dishwasher or sink close to the DB but wondered if I can have an eye level oven below it.
    I see that the rules say that it is possible as long as there is protection between the two.
    What constitutes protection?
    I don’t want to install and then do not get an electrical compliance certificate in future.

    Thank you in advance for the advice.

  2. #2
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,041
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Without even going into the regs, common sense would tell me installing an ELO below a DB would create restricted access to the main switch and the earth leakage unit, make sure you put a clip on the side of the ELO so that you can use a broom stick to switch on the breakers (seems to be the norm).

    The height would need to be taken into consideration.

    A IP rating would have been considered, however the ELO is contained in a cupboard or exhausted out the front of the unit, there shouldn't be a moisture problem directly above the ELO

  3. #3
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    If you are installing an oven, then it will have to be connected to the electricity, presumably via a new installation and switch.
    The work will have to be done, or at least supervised, by a certified and registered electrician.
    The electrician doing the work will have to provide you with an electrical compliance certificate once the work is completed, that is the law.

    That electrician will advise on the safety aspects required.

    Sent from my SM-A528B using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  4. #4
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,041
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Lets say the DB is less than 2.5 m AFFL and you fit the stove isolator next to the ELO as per the latest SANS 10142-1-2021-(ed3.01).

    Installing a cupboard below the DB, making in impossible to reach it without the use of a chair or the like, would you issue a COC?

    The way I see it the main switch is not within arms reach.

    The same thing with many installations were a huge double door fridge is directly in front of the DB, the fact that the DB is at 1.8 m behind the fridge doesnt make it accessible "in case of an emergency". To make it even more inaccessible people install a cupboard above the fridge, so you have to remove the fridge to gain access .

  5. #5
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,510
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Quote Originally Posted by SueRi View Post
    Hi
    I am starting a renovation of a small apartment kitchen soon and the DB is in a position that makes it difficult. I know I can’t have a dishwasher or sink close to the DB but wondered if I can have an eye level oven below it.
    I see that the rules say that it is possible as long as there is protection between the two.
    What constitutes protection?
    I don’t want to install and then do not get an electrical compliance certificate in future.

    Thank you in advance for the advice.
    2 options.

    1. DB may be out of reach as long as the switch disconnector is below 2,2m from floor level and is easily reachable.
    The isolator for the DB does not need to be in the DB. (6.6.1.6)

    2. DB may be above a cooking appliance if the enclosure provides a degree of protection of at least IP44.
    A shallow wooden cupboard with door to cover the DB will suffice. (6.6.1.7.b)

  6. #6
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,041
    Thanks
    55
    Thanked 97 Times in 93 Posts
    Quote Originally Posted by Derlyn View Post
    2 options.

    1. DB may be out of reach as long as the switch disconnector is below 2,2m from floor level and is easily reachable.
    The isolator for the DB does not need to be in the DB. (6.6.1.6)

    2. DB may be above a cooking appliance if the enclosure provides a degree of protection of at least IP44.
    A shallow wooden cupboard with door to cover the DB will suffice. (6.6.1.7.b)
    You will battle to fit an eye level oven in a shallow wooden cupboard

    Why no just fit an under counter oven and make sure the DB is at least IP 44 rated ?

    Just makes the main switch accessible.

  7. #7
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,510
    Thanks
    106
    Thanked 146 Times in 139 Posts
    The DB needs to be in a shallow cupboard, not the oven.

  8. #8
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,510
    Thanks
    106
    Thanked 146 Times in 139 Posts
    The shallow cupboard over the DB makes it IP44.

  9. #9
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,659
    Thanks
    3,307
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    Appealing to the designer (seeing as this is still at the design stage), which is more important to the end user - form or function?
    May I suggest the correct answer is BOTH.

    Can I appeal to you - keep the DB easily accessible. There will be times when the end user will sincerely appreciate it.
    How can we get the form we want with the eye level oven off to one side of the DB?
    There are always options.

Similar Threads

  1. Definition of distribution board.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 19-Feb-22, 07:56 AM
  2. Distribution board isolator
    By ians in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 16-Dec-21, 10:42 AM
  3. Moving a distribution board.
    By Leslie Clark in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 08-Oct-17, 02:26 PM
  4. [Question] Fused distribution board
    By pes in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 11-Aug-13, 08:01 AM
  5. Distribution board over toilet
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 26-Jul-12, 09:22 PM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •