When is a double pole isolator required for a fan
    [Question] When is a double pole isolator required for a fan
    I believe this requires a thread on its own.
    When is a double pole isolator required?
    Lets use a common application ... the extractor fan connected to the light in the bathroom ... do you need a double pole isolator for this application if the light circuit is on earth leakage?
    A ceiling fan in a bedroom with a light ... do you need a double pole isolator if the light circuit is connected to the earth leakage ?
    If the extractor fan is in a bathroom but not connected via the light fitting?
    can you fit the double pole isolator in the roof next to the fan ?
    Can you use a 5 amp socket outlet instead of a double pole isolator ...between the light and the extractor fan?
    Can you use a standard socket outlet for the extractor fan located out of reach in the ceiling.
    can you use a combo breaker/isolator in the DB to feed the light circuit made up of lights and extractor fans.
    I am sure the reare other questions related to this topic.
  • Dylboy
    • Jun 2020
    • 777
    Also if the CB is a single pole but the correct markings for isolation then does it have to be double pole?
    Unless it specifically states to use a double pole or that the LIVE (N & L) must be switched.
    • W-TDMI
      • May 2013
      • 39
      All your answers is in the following sub sections:
      6.9.2 but more specific 6.9.3.1 and 6.16.1.3 and 6.16.1.4
      In short if its on E/L no isolator is required - If no E/L must have isolator 1.5m from fan OR Lockable in the open position if in the DB.
      ~INSPECT, TEST, VERIFY, CERTIFY~
        What if you replace the light switch with a double pole and it is not 1.5m because the fan is the slab... but in the same room or at the entrance to the room/bathroom ?
        Or in a case where I had no choice but to fit a double pole relay/contactor ... has 30 amp double pole relay got the isolation properties of a manual isolator ?
          • 1482
          I disagree - A fan is a motor and falls under motor - A lockable in a DB will not be acceptable
          6.16.4.3 Extraction fans
          Where an extraction fan supply is switched with a luminaire, it shall be
          connected to the switched portion of the light circuit, provided that the fan
          circuit is connected by means of a SANS 164-3 or SANS 164-2-1 or
          SANS 164-2-2 socket-outlet or a switch disconnector.
          6.16.5.1.4 Each motor shall be supplied by a manually operated disconnector
          or any other manually operated disconnecting arrangement such as a
          withdrawable circuit-breaker, a removable link, a fuse or by the removal of a
          plug from a socket-outlet, which provides at least the same isolating distance,
          for the sake of safety, as a disconnector that is
          b) visible from the motor, or
          d) housed in a lockable enclosure other than a distribution board.
            For the record the plugs GCE refers to are found on page 335 ,,, annexure R.