Originally Posted by
Dylboy
It appears I need some work on this and what I was taught in my apprentice days may not be correct.... anyways,
So here is my process... back to basics so here is a every day sorta situation...
A 2.5mm flat twin and earth cable which has a 1.5mm CPC (Earth) on a 20A CB. How long can I run this cable? ( assume a 10A load at the end)
If i do the Rmax = v / 2 x I I get 5.75 ohms.
If I then apply it to Recc = p x L / A
(A being 1.5mm˛ as doing line to E fault) I get a length of 386 meters...
If I do the Touch Vtage formula so as to keep it to 30V ( in book says do calcs at 30V )
TV= 2 x I x R
30 = 2 x 20 x R
30= 40 x R
R = 0.75 ohm
Then again the Recc formula to calc length
Recc = P x L / A (A being 1.5mm˛)
0.75 = 0.0223 x L / 1.5
Legth = 50meters
Then on page 168 of Ed 3.0 has the formula for the max length of the Ecc (CPC, Earth)
And when i do that with the 0.8 factor out i get 48meters (closer to the TV side of 50 meters)
Then the bloody table above also has very low Ohm ranges haha.
So anyone wiser than me on this know the best answer or method to determine that question ?
Also in section 8 it says that if the Recc can not be checked (long wonder lead) then the method for the loop test must be done which then included the Rmax formula which is 5.75ohm, I know it then has a loop so "double distance) and the phase and Earth are diffenrft CSA so not sure how to get that to a single Earth restaince number to try do the math...
I am down a rabbit hole at the moment with all this as need to prove to current boss that there may be an issue in the design but I want to make sure I am not to far gone and lost...
Edit: Vd excluded at this time, as could be a 5A load but this is just for some math and getting out the rabbit hole.
Edit again: had a brain wave at 1 this morning when small was awake that the TV formula I use is the same as the Rmax formula.... so the diffenrce then being the voktage of either 230v or 30v
Sent from my SM-N960F using Tapatalk