    3.9.2 flexible cable
    cable of which the conductors consist of strands of diameter not exceeding 0,51 mm and of which the insulation and covering are such that they afford flexibility and in which the nominal cross-sectional area of each conductor exceeds 4 mm²

    How do you understand the rule above?

    How does this apply to Twin&Earth or GP wire?

  2. #22
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,260
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Quote Originally Posted by Dave A View Post
    Just checking for clarity (because in Durban at least and as I understand, in the majority of metros in SA we are on TN-S supplies) - are you differentiating between cable armour being used instead of a dedicated earth conductor, or is it uncommon for you to have TN-S supplies in your part of the country?
    We are TN-C- S

    Generally municipalities only run the last bit , +/- 70m of copper earth before the sub with earth spikes and on bigger supply's the same story before the premises

    It will not be solid copper or even armour cable earth all the way

    Some of the lead cables they do - It is hit and miss

  3. #23
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,260
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Quote Originally Posted by Lourens.dL View Post
    3.9.2 flexible cable
    cable of which the conductors consist of strands of diameter not exceeding 0,51 mm and of which the insulation and covering are such that they afford flexibility and in which the nominal cross-sectional area of each conductor exceeds 4 mm²

    How do you understand the rule above?

    How does this apply to Twin&Earth or GP wire?
    I read it as the normal cabtyre being flexible cable or trailing cable

  4. #24
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,260
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Quote Originally Posted by Dylboy View Post
    Now that is intresting and changes everything, thank you! I did not realise it was for the armouring as that is also not copper so then yes some different maths.

    The bit in red I just saw as a supplementary earthing conductor of copper and didn't think of it being SWA.
    on ECC armour cable there are stands of armouring that are replaced with tinned copper strands to accommodate the correct earth readings - It is then manufactured according to a standard and the amp rating of the copper phases in spec to accommodate the potential earth fault on the copper strands taking into account the surface area to dissipate the potential build up of heat on a fault

    https://www.actomep.co.za/pvc-mains-...per-cable-50mm

  5. #25
    Junior Member
    Join Date
    Apr 2014
    Location
    Westrand
    Posts
    23
    Thanks
    6
    Thanked 2 Times in 2 Posts
    Quote Originally Posted by GCE View Post
    I read it as the normal cabtyre being flexible cable or trailing cable
    Note that flexible cable must exceed 4mm².

    Would cabtire not fall under flexible cord?
    3.9.3 flexible cord
    cable of which
    a) the nominal cross-sectional area of each conductor does not exceed 4 mm², and
    b) each conductor consists of strands of diameter less than 0,31 mm


    The point I'm trying to make is per definition neither GP wire or Twin&Earth or Airdac or Surfex etc can be classified as a flexible cable or flexible cord.

    Sent from my SM-N975F using Tapatalk

  6. #26
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Quote Originally Posted by GCE View Post
    on ECC armour cable there are stands of armouring that are replaced with tinned copper strands to accommodate the correct earth readings - It is then manufactured according to a standard and the amp rating of the copper phases in spec to accommodate the potential earth fault on the copper strands taking into account the surface area to dissipate the potential build up of heat on a fault

    https://www.actomep.co.za/pvc-mains-...per-cable-50mm
    Yes I can see that table working for the those but the everyday SWA we use is all metal so then we would have to work with the manufactures specs.

    Sent from my SM-N960F using Tapatalk

  7. #27
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,260
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Quote Originally Posted by Lourens.dL View Post
    Note that flexible cable must exceed 4mm².

    Would cabtire not fall under flexible cord?
    3.9.3 flexible cord
    cable of which
    a) the nominal cross-sectional area of each conductor does not exceed 4 mm², and
    b) each conductor consists of strands of diameter less than 0,31 mm


    The point I'm trying to make is per definition neither GP wire or Twin&Earth or Airdac or Surfex etc can be classified as a flexible cable or flexible cord.

    Sent from my SM-N975F using Tapatalk
    Apologies - Yes cabtyre would be flexible cord.

    T&E , Airdac , surfix etc would be classified as cable and to strengthen the point I have pasted the headings that I see as surfix and T&E wherein they refer to cables - Then the earth would beclassified under 6.12.1.1b

    6.3.6 PVC insulated multicore cables with a bare earthing conductor
    and round cable with metal stiffening
    6.3.6.1 The cables may be installed
    a) on the surface,
    b) under plaster,
    c) under a raised floor,


    6.12.1.1 An earth continuity conductor shall
    a) consist of compatible conductors,
    b) if it forms part of a cable other than a flexible cable, comply with the relevant
    requirements of the standard for the cable,
    c) if it forms part of a flexible cable, be of the same material as, and have a
    nominal cross-sectional area at least equal to, that of the largest phase
    conductor,
    d) be able to carry the prospective fault current without excessive temperature
    rise of the conducor, within the disconnecting time
    e) if it does not form part of a cable or flexible cable, have a nominal crosssectional
    area at least equal to that determined in accordance with
    table 6.28(a), as follows:

  8. Thanks given for this post:

    Lourens.dL (25-Jan-22)

  9. #28
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,260
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Quote Originally Posted by Dylboy View Post
    Yes I can see that table working for the those but the everyday SWA we use is all metal so then we would have to work with the manufactures specs.

    Sent from my SM-N960F using Tapatalk
    I see normal armour cable as outside of 6.12.1.1 and I have highlighted in red the way I would read it - Normal armour cable does not have an earth continuity conductor and you need to look at the note under 6.12.1.4.

    6.12.1 Earth continuity conductors
    6.12.1.1 An earth continuity conductor shall
    a) consist of compatible conductors,
    b) if it forms part of a cable other than a flexible cable, comply with the relevant
    requirements of the standard for the cable,
    c) if it forms part of a flexible cable, be of the same material as, and have a
    nominal cross-sectional area at least equal to, that of the largest phase
    conductor,
    d) be able to carry the prospective fault current without excessive temperature
    rise of the conducor, within the disconnecting time
    e) if it does not form part of a cable or flexible cable, have a nominal crosssectional
    area at least equal to that determined in accordance with
    table 6.28(a), as follows:

    NOTE The information in 6.12.1.4 also applies to wire armouring if it is used as the
    earth continuity path provided it meets the comparable resistance values of the
    equivalent earthing continuity conductor and the armour wires are all correctly
    terminated using an earthed metal captive coned gland; it may be necessary to replace
    some of the steel wires with tinned copper ones or to use a supplementary earth
    continuity conductor

  10. Thanks given for this post:

    Lourens.dL (25-Jan-22)

  11. #29
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,260
    Thanks
    34
    Thanked 305 Times in 259 Posts
    Quote Originally Posted by Dylboy View Post
    Happy Friday all!

    Anyone know the formula used for the attached screenshot ? (The table )

    The numbers in Ed 2 are different to Ed 3.0

    Also I was taught to do the touch voltage formula to get the Recc

    Just want to dive deeper into this

    To Answer the original question I would say that section 6.121.1.1 (3) gives you the calculation to get to maximum resistance values of the earth continuity conductor -

    3) where the maximum length of the conductor may be determined using
    the following equation
    Lmax=
    0,8×Uo×Sph
    ρ(1+m)×Im
    where
    Uo is the phase voltage of 230 V,
    ρ is the resistivity at normal working temperature in ohm.mm2/metre
    which is 23 × 10-3 for copper which value increases above 120 mm2
    with R+15 % (150 mm2), R+20 % (185mm2), R+25 % (240mm2) and
    R+30 % (300 mm2),
    Lmax is the maximum length of the conductor in metres (m);
    Sph is the size of the phase conductor in square metres (mm2);
    Spe is the size of the earth continuity conductor in square metres
    (mm2);
    Im is the instantaneous or short time tripping current in amperes (A).
    For most general purpose circuit breakers it would suffice to use
    10 multiply by the rated nominal current In for the instantaneous
    tripping point of the circuit breaker, however the precise number could
    be obtained from the manufacturer's information or from the
    instantaneous current setting of adjustable circuit breakers, thus
    𝐼𝑚 = 𝐼𝑛 × 10
    Correction factor m =
    𝑆𝑝ℎ
    𝑆𝑝𝑒
    = 1 [for table 6.28 (a)]
    f) using the same formulae above where the earth continuity conductor
    cross sectional area is 50 % of the phase conductor, thus m = 2,
    table 6.28(b) for the maximum length of copper earth continuity
    conductor for general purpose circuit breaker apply.

  12. Thanks given for this post:

    Dylboy (25-Jan-22)

  13. #30
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Quote Originally Posted by GCE View Post
    To Answer the original question I would say that section 6.121.1.1 (3) gives you the calculation to get to maximum resistance values of the earth continuity conductor -

    3) where the maximum length of the conductor may be determined using
    the following equation
    Lmax=
    0,8×Uo×Sph
    ρ(1+m)×Im
    where
    Uo is the phase voltage of 230 V,
    ρ is the resistivity at normal working temperature in ohm.mm2/metre
    which is 23 × 10-3 for copper which value increases above 120 mm2
    with R+15 % (150 mm2), R+20 % (185mm2), R+25 % (240mm2) and
    R+30 % (300 mm2),
    Lmax is the maximum length of the conductor in metres (m);
    Sph is the size of the phase conductor in square metres (mm2);
    Spe is the size of the earth continuity conductor in square metres
    (mm2);
    Im is the instantaneous or short time tripping current in amperes (A).
    For most general purpose circuit breakers it would suffice to use
    10 multiply by the rated nominal current In for the instantaneous
    tripping point of the circuit breaker, however the precise number could
    be obtained from the manufacturer's information or from the
    instantaneous current setting of adjustable circuit breakers, thus
    𝐼𝑚 = 𝐼𝑛 × 10
    Correction factor m =
    𝑆𝑝ℎ
    𝑆𝑝𝑒
    = 1 [for table 6.28 (a)]
    f) using the same formulae above where the earth continuity conductor
    cross sectional area is 50 % of the phase conductor, thus m = 2,
    table 6.28(b) for the maximum length of copper earth continuity
    conductor for general purpose circuit breaker apply.
    Yes ya I saw that formula and did the calculations for it at the top and if I don't use the 0.8 factor (I assume to counter variances in tempreture) I get 48meters which works close with the Touch voltage formula which does not include tempreture variations.



    Sent from my SM-N960F using Tapatalk

Page 3 of 4 FirstFirst 1234 LastLast

Similar Threads

  1. [Question] Formula to calculate leave due in Excel
    By Helizelb in forum Accounting Forum
    Replies: 13
    Last Post: 20-Nov-22, 12:40 PM
  2. [Question] How do i calculate value n category share.
    By yrstruly in forum Marketing Forum
    Replies: 0
    Last Post: 16-Mar-21, 07:32 PM
  3. how to calculate notional rent
    By Maijane in forum Accounting Forum
    Replies: 0
    Last Post: 24-Jun-20, 01:19 PM
  4. [Question] Calculate Fair Value and Reserve Value
    By JPWilliams007 in forum Accounting Forum
    Replies: 1
    Last Post: 28-Nov-19, 10:10 AM
  5. Formula to calculate staff costs against profit
    By Jacky in forum Accounting Forum
    Replies: 4
    Last Post: 23-Oct-14, 09:17 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •