    Brain fart, 3phase

    Hello all!

    Hope its a good Tuesday.

    I am having a bit of a brain fart and I guess a bit sleep deprived from the little one.

    But below image i have drawn is a 3phase supply then supplying 3 x single phase main switches, your typical 3 phase house...

    Now my brain is not working on:

    - can each phase pull lets say 60Amps each and not trip the CB as it is rated at 80Amps
    Or will the combined amps which is over 80A trip the CB. ?

    Essentially is the 3phase CB like 3 single pole breakers joined, so each "single pole" has the trip at 80Amps thus allowing each of the phases to pull a max of 80Amps? And if one of them trips it then trips the whole CB ?

    Apologies if this is basic but I am having a struggle today.



    Sent from my SM-N960F using Tapatalk

  2. #2
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    The three phase breaker is actually three separate breakers joined together mechanically. Unless it has only one handle then it is constructed differently but works the same.

    Sent from my SM-A705FN using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  3. Thanks given for this post:

    Dylboy (18-Jan-22)

  4. #3
    Junior Member
    Join Date
    Apr 2014
    Location
    Westrand
    Posts
    23
    Thanks
    6
    Thanked 2 Times in 2 Posts
    Just to add, each of the three beakers is rated at 80A and if one phase overload then all will trip.

    Sent from my SM-N975F using Tapatalk

  5. Thanks given for this post:

    Dylboy (18-Jan-22)

  6. #4
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    759
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Ahhh ok brilliant, I thought as much, thanks gents, really appreciate it !

    Sent from my SM-N960F using Tapatalk

  7. #5
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,480
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Quote Originally Posted by Lourens.dL View Post
    Just to add, each of the three beakers is rated at 80A and if one phase overload then all will trip.

    Sent from my SM-N975F using Tapatalk
    You would not have it any other way, switching one phase off on a 3 phase load is detrimental to the equipment, unless it is a heater bank
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

Similar Threads

  1. [Question] 3phase domestic SPD protection
    By Clive287 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 20-Apr-15, 06:53 AM
  2. brain teaser
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 21-Feb-10, 09:52 PM
  3. MTN - are they all brain dead?
    By Sieg in forum General Business Forum
    Replies: 25
    Last Post: 18-Jul-09, 04:32 PM
  4. Zimbabwe seeks to reverse brain drain.
    By Dave A in forum General Business Forum
    Replies: 0
    Last Post: 10-Oct-06, 06:19 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •