    In SANS 10142-1:2020, there are 2 tables with same description but different values: Table 6.28(a) and 6.28(b). Why the difference, when should which table be used? It can make a big difference in price when big building is involved with 800A circuit breakers.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,246
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Quote Originally Posted by PC Bester View Post
    In SANS 10142-1:2020, there are 2 tables with same description but different values: Table 6.28(a) and 6.28(b). Why the difference, when should which table be used? It can make a big difference in price when big building is involved with 800A circuit breakers.
    There is a difference in table description as can be seen from the headings pasted below from SANS
    The explanation and calculations for Table 6.28(b) precedes the table
    The clause below extracted from SANS sums up the difference between the 2 tables

    For most general purpose circuit breakers it would suffice to use
    10 multiply by the rated nominal current In for the instantaneous
    tripping point of the circuit breaker, however the precise number could
    be obtained from the manufacturer's information or from the
    instantaneous current setting of adjustable circuit breakers, thus
    Im=In x 10


    Table 6.28(a) — Minimum size and maximum length of copper earth continuity conductors rated at phase conductor
    diameter, for general purpose circuit-breaker

    Table 6.28(b) — Minimum size and maximum length of copper earth
    contuinity conductors rated at 50 % of phase conductor diameter, for
    general purpose circuit-breakers with instantaneous tripping current
    Im = 10 × In

  3. #3
    New Member
    Join Date
    Jan 2022
    Location
    Bloemfontein
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Tnx very much, that gives me more clarity. I appreciate.

Similar Threads

  1. [Question] Earth Tag as Earth Continuity Conductor
    By Matt.24 in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 07-Oct-21, 09:02 AM
  2. Earth continuity conductors
    By ians in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 08-Apr-21, 01:39 PM
  3. no earth conductors in home installation
    By markthespark in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 30-May-19, 09:27 AM
  4. Bank Account Continuity
    By pete9999 in forum Accounting Forum
    Replies: 7
    Last Post: 29-Jun-17, 08:00 PM
  5. [Question] electrical earth continuity
    By Groen Karoo in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 14-Sep-11, 08:07 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •