Can I bounce something off you guys, who are up to speed with the domestic SANS codes.
Client of mine had an expensive pump & tank system fitted as a mains water backup, Joburg Northern suburbs. Top $ client. Fancy kit.
Its located by entrance gate and direct adjacent to the enclosure that has the City Power meter.
What the electrician who was called in to do the electrical work did is connected the small sub db they installed direct to the point of supply board, to one phase coming out the smart meter, via a single pole circuit breaker
My understanding is that this is not on and is non complaint with the 10142 codes, circuits have to be downstream of the main switch. There can only be one main switch. If you turn that off you expect all the circuits to be dead.
Reason why they did this: its right there, taking a cable to the house is work and expenses. And who would give a damn anyway.
Can anyone confirm or comment please. Thanks in advance.
I might need some help with a formal report from a Master Electrician who is around this area.
If this a problem, getting it sorted out is easy, but what about the guys that did this? There sticker is on the sub db box. I see soooo much horrible unsafe work around (that often gets CoC'sl), there really should be repercussions guys are getting away with it. Or is that the world we live in.