Thread: RCD and AFDD

  1. #1
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts

    RCD and AFDD

    This is something which is going to need to be addressed soon.

    The days of walking into a wholesaler and picking up the cheapest type A RCD is just not going to cut it anymore ... it could also explain why there are so many complaints about random tripping ... due to incorrect selection of the RCD required for the application.

    Once you have done a little research into RCD types ... then you going to find there is a device which might suit the application better or create even more problems ... an AFDD

    As I am researching alternative supplies ... looking at how people are installing (RCD) or commonly known as a earth leakage device in P.1 - P.4 ... throw in a bonded neutral/earth and relays for bonding neutral and earth ... it makes you wonder if the correct type of RCD has been selected ?

    Anyone here have a lot of experience using the different types of RCD's and AFDD's ?
    Comments are based on opinion...not always facts....that's why people use an alias.

  2. #2
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Do you have to install an RCD before the inverter or UPS.

    Common sense in the past would have me "not" connecting a UPS to an RCD circuit ... the reason ... a UPS was used for dedicated socket outlets for computers and stuff ... however since load shedding started people use any means to try keep the lights on.

    Do you have to connect an inverter to an RCB circuit?

    I have noticed while going through tons of information ... one inverter distributor indicates the use of a type A RCB is required.

    If the manufacturer/supplier recommends you connect the inverter to an RCD ... would it affect the warranty if not installed ... and how do they deal with random tripping issues?

    Is a type A RCB best suited for that application ... is it recommended by the RCD supplier ?
    Comments are based on opinion...not always facts....that's why people use an alias.

  3. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Then we need to start digging into neutral earth bonding and the effects it has on RCD's and the location of the RCD in the circuit.

    Some inverters require an external neutral/earth bridge ... and an RCD at the inverter.
    Comments are based on opinion...not always facts....that's why people use an alias.

  4. #4
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    759
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Do we even get the type A and AC And F etc RCDs in the country ?

    But yes the N and E bond is an issue. We found a solar install the other day where this needs a grounding box.
    I then tested my inveter yesterday with simulated mains fail of main switch and then cranked a socket and my ELU did not trip... I have an ELU to feed inverter and output of inveter is another ELU. Waiting for grid to go down to rest again as my main switch is an ELU and kn the complex which is old I have no access to my feed switch.

    But in the end I am getting a grounding box soon as I saw my N was floating...

    Live and learn everyday and glad found this out now on the inverter.

    This inveter stuff and solar is new to many an electrician and not everyone is keen on sharing info or "secrets"

    Sent from my SM-N960F using Tapatalk

  5. #5
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    What may seem like a silly question I am sure many people are thinking ... if you have a bi directional system (hybrid inverter) if you power is being fed from the mains to the inverter the way line and load breakers are designed to work ... when you feed the power back from the inverter to the RCD ... is it not the same thing as plugging a generator using the suicide cord system?

    I was under the impression ... the reason the suicide cord was so dangerous was because the power is flowing in the wrong direction and therefore creates a dangerous environment because the safety devices in the electrical installation will no longer function correctly ?
    Comments are based on opinion...not always facts....that's why people use an alias.

  6. #6
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    759
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Quote Originally Posted by ians View Post
    What may seem like a silly question I am sure many people are thinking ... if you have a bi directional system (hybrid inverter) if you power is being fed from the mains to the inverter the way line and load breakers are designed to work ... when you feed the power back from the inverter to the RCD ... is it not the same thing as plugging a generator using the suicide cord system?

    I was under the impression ... the reason the suicide cord was so dangerous was because the power is flowing in the wrong direction and therefore creates a dangerous environment because the safety devices in the electrical installation will no longer function correctly ?
    Not thought of it that way before... I feel their would be an overcurrent device along the conductor so that should be fine but then isolation could be an issues as you isolate to bottom of switch but now the electrikery is now coming back side to whack you... I guess when maintenance switch off and isolate everything haha

    Sent from my SM-N960F using Tapatalk

  7. #7
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,480
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Quote Originally Posted by ians View Post
    What may seem like a silly question I am sure many people are thinking ... if you have a bi directional system (hybrid inverter) if you power is being fed from the mains to the inverter the way line and load breakers are designed to work ... when you feed the power back from the inverter to the RCD ... is it not the same thing as plugging a generator using the suicide cord system?

    I was under the impression ... the reason the suicide cord was so dangerous was because the power is flowing in the wrong direction and therefore creates a dangerous environment because the safety devices in the electrical installation will no longer function correctly ?
    Not quite so.
    The inverter only feeds back to the loads connected on the incoming side of the inverter, if it has excess energy to share. Once the mains goes down, then this function desists, as an internal relay in the inverter will disconnect the inverter from the supply.

    This is also known as "Anti Islanding"

    What is Anti-Islanding? Anti-Islanding is the ability to quickly stop sending power into the grid from your solar system. Here's Why Anti-Islanding is important: Electric utility companies refer to residential grid-tie solar power arrays as distributed generation (DG) generators.
    Islanding
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  8. #8
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Thinking out loud ... the suicide cord is dangerous because it feeds back into the grid ... which could result in injury to council works or anyone upstream ... it has nothing to do with the direction of flow?

    The fact that the one side of the plug top has live exposed conductors (I have a site where the generator installer has fitted a male plug top to the generator) I have advised the customer of the danger ... however the installer assured the customer that it is fine ... ok.
    Comments are based on opinion...not always facts....that's why people use an alias.

  9. #9
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,480
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Quote Originally Posted by ians View Post
    Thinking out loud ... the suicide cord is dangerous because it feeds back into the grid ... which could result in injury to council works or anyone upstream ... it has nothing to do with the direction of flow?
    My thinking is if this is in a residential area, and the user has the isolator in the on position, the little generator will be overloaded, as it tries to power up all the loads connected to that line on the municipal side, unless it is a big genny then yes there could be a voltage going back, but I think by that time either the extension has burnt out or the circuit breaker would have tripped.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  10. #10
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,484
    Thanks
    104
    Thanked 141 Times in 134 Posts
    With a suicide cord, the earth leakage does not work and all other plugs on the same circuit as the one you are backfeeding into, have no protection.

    Not a healthy situation.

    Peace out .. Derek