Thread: New SANS 10142-1:2021 (ed. 3.o1)

  1. #21
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    8.6.2 Continuity of bonding
    Confirm the continuity of the bonding conductors between all exposed
    conductive parts within arms reach (or see annex A) of each other. When a
    test device or instrument is used, it shall have a supply that has a no‐load d.c.
    or a.c. voltage of 4 V to 24 V, and a current of at least 0,2 A. In each case, the
    resistance shall not exceed 0,2 Ω. Amdt 1
    Comments are based on opinion...not always facts....that's why people use an alias.

  2. #22
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    8.6.7 Earth resistance
    8.6.7.1 Earth resistance can be determined in accordance with SANS 10199.
    NOTE Where the supplier does not provide an earthing terminal or where an
    alternative supply is installed, the efficiency of the earthing system can be confirmed by
    this test in SANS 10199 or by using an appropriate instrument. Amdt 1
    Comments are based on opinion...not always facts....that's why people use an alias.

  3. #23
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    8.7 Test reports
    The following test reports are applicable:
    a) Test report for all electrical installations, excluding secondary reticulation,
    NOTE This report may be supplemented with the additional report for a medical
    location. Amdt 1
    b) Test report for secondary reticulation per 7.16,
    c) Additional test report for electrical installations in medical location in
    accordance with SANS 10142-1-1, and Amdt 1
    d) Inspection and test report for electrical installations in hazardous locations
    Comments are based on opinion...not always facts....that's why people use an alias.

  4. #24
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    It quite handy having 3.0 and 3.1 in pdf ... you can tile them and scroll down to see the amendments.

    You would think they would check the document for errors prior to releasing them
    Comments are based on opinion...not always facts....that's why people use an alias.

  5. #25
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    That people is what you gonna piss another R1000 + against the wall to receive ...what a waste of R1000

    I have included the slights change to the test report because that will be on any new test report you purchase.

    I have another draft for new regulations ... the only reason I wasted the money ... I thought a lot of the stuff in that draft would be in this update ... once again you live and learn and waste money.
    Comments are based on opinion...not always facts....that's why people use an alias.

  6. #26
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    759
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Ians you are a hero! Thank you! when ever we cross paths a lunch is on me.

    Sent from my SM-N960F using Tapatalk

  7. #27
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    This what you are paying over a R1000 for

    (ED3.0)
    3.31
    electrical consultant
    person who is registered in terms of the Engineering Profession Act, 2000 (Act
    46 of 2000)

    (ED3.1)
    3.31
    electrical consultant
    person who is registered in terms of the relevant national legislation
    (see foreword) Amdt 1

    huge amendments ... I can only sit here and smile
    Comments are based on opinion...not always facts....that's why people use an alias.

  8. #28
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I sat read the entire PDF to see where the 19 pages were missing ... The pages missing are related to medical locations ... an example annex L is gone.
    Comments are based on opinion...not always facts....that's why people use an alias.

  9. #29
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    For the record ... I did check the document properties

    Document restriction summary

    Printing = allowed
    Content = copying allowed
    Comments are based on opinion...not always facts....that's why people use an alias.

  10. #30
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,649
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by ians View Post
    6.16.3.3.3 The stove connections may be wired directly between the isolator
    and the stove terminals, by means of a flexible arrangement, which are
    mechanically secured and be terminated on either end. When the stove is
    removed, the final section of hard wiring to the stove terminals has to be
    removed and made safe. Amdt 1
    At long last!!
    An option to the stove coupler (which is not available for love or money )

Page 3 of 6 FirstFirst 12345 ... LastLast

Similar Threads

  1. SANS 10142-1 (ed3)
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 23-Apr-21, 06:29 AM
  2. SANS 10142-1:2017 (Ed. 2.00)
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 27
    Last Post: 23-Oct-18, 06:56 AM
  3. SANS 10142 Edition 2
    By Karel Kriel in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 02-Jul-17, 08:20 AM
  4. sans 10142-1:2012
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 23-Apr-13, 05:56 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •