Thread: New SANS 10142-1:2021 (ed. 3.o1)

  1. #11
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    3.31
    electrical consultant
    person who is registered in terms of the relevant national legislation
    (see foreword) Amdt 1

    Distribution boards ≤ 10 kA short-circuit current low-voltage
    switchgear and controlgear
    Assemblies > 10 kA
    For outdoor use and exposed to public
    Assemblies for construction sites
    SANS 1973-3
    SANS 1973-1 or SANS 61439-2
    SANS 61439-5
    SANS 61439-4

    5.3.2 Voltage drop
    5.3.2.1 When all conductors of an a.c. installation are carrying their maximum
    estimated load, the difference in voltage (the voltage drop) between the point
    of supply and any point of outlet or terminals of fixed appliances shall not
    exceed 5 % of the standard voltage or of the declared phase-to-neutral
    voltage (see also 6.2.7).

    f) where the distribution board is concealed by a cupboard or other covering,
    the notice for live electrical apparatus referred to in annex N shall be in a
    conspicuous place indicating the position of the distribution board.

    5.4.2 Voltage
    The equipment shall be suitable for operation on the maximum steady (r.m.s.)
    voltage and overvoltage to which it is likely to be subjected. Equipment shall
    be rated in accordance with the intended application for use on one of the
    following voltages used in South Africa:
    a) A.C. circuits:
    1) standard voltages at a point of supply of Amdt 1


    6.2.3 Basis of tabulated current-carrying capacity
    6.2.3.1 The current-carrying capacity of conductors and cables set out in this
    clause takes account of IEC standards, where applicable. For types of cable
    not covered in the relevant IEC publication (for example, armoured cables)
    the current-carrying capacity given in this clause is based on data provided by
    the relevant national association (see foreword). Amdt 1
    Comments are based on opinion...not always facts....that's why people use an alias.

  2. #12
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    6.2.7 Voltage drop
    6.2.7.1 Difference in voltage (voltage drop)
    6.2.7.1.1 When all conductors of an a.c. installation are carrying their design
    load, the difference in voltage (the voltage drop) between the point of supply
    and any point of outlet or terminals of fixed appliances shall not exceed 5 %
    of the standard or declared voltage. (See 5.3.2, 5.4.2 and annex D.)
    6.2.7.1.2 In the case of a 230/400 V system, the voltage drop for single-phase
    circuits shall not exceed 11,5 V (5 % of 230 V) and the voltage drop for
    three-phase circuits shall not exceed 20 V (5 % of 400 V). Amdt 1
    6.2.7.1.3 In the case of single-phase circuits derived from three-phase
    supplies with balanced loading, the phase-to-neutral voltage drop is calculated
    from three-phase values divided by
    3 . Amdt 1
    6.2.7.1.4 For multiple installations connected in series (for example housing
    schemes, etc) refer to 5.4.2 for overal voltage drop requirements. Amdt 1
    NOTE 1 If the phase-to-neutral voltage is not declared, the value can be calculated by
    dividing the phase-to-phase voltage by 1,73.
    NOTE 2 Deleted by amendment No. 1.
    6.2.7.1.5 When all conductors of a d.c. installation are carrying their
    maximum estimated load, the difference in voltage (the voltage drop) between
    any point of supply and any point of consumption shall not exceed 5 % of the
    circuit nominal voltage or shall comply with the requirements of the
    manufacturer of the equipment connected to the circuit. Amdt 1
    Comments are based on opinion...not always facts....that's why people use an alias.

  3. #13
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    6.5.2.2 Electrical continuity
    Rigid metallic wireways shall be electrically continuous and be connected to
    earth as close as possible to the source. Amdt 1
    Comments are based on opinion...not always facts....that's why people use an alias.

  4. #14
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Table 6.22 is also marked as an amdt 1 ...it looks like they fixed the table which was missing 4 mm/16mm/50mm
    Comments are based on opinion...not always facts....that's why people use an alias.

  5. #15
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    NOTE It is recommended that earth leakage protection be installed in all circuits
    that supply socket-outlets in existing installations prior to earth leakage becoming
    compulsory. Amdt 1

    6.7.7 External lightning protection
    NOTE Where external lightning protection is installed, it should be in accordance with
    the requirements of SANS 10313. Amdt 1

    6.12.1 Earth continuity conductors
    6.12.1.1 An earth continuity conductor shall
    a) consist of compatible conductors,
    b) if it forms part of a cable other than a flexible cable, comply with the relevant
    requirements of the standard for the cable,
    c) if it forms part of a flexible cable, be of the same material as, and have a
    nominal cross-sectional area at least equal to, that of the largest phase
    conductor,
    d) be able to carry the prospective fault current without excessive temperature
    rise of the conductor, within the disconnecting time,
    e) if it does not form part of a cable or flexible cable, have a nominal
    cross-sectional area in accordance with table 6.25 and if it equals to the
    phase conductor size refer to table 6.28(a), as follows: Amdt 1
    Comments are based on opinion...not always facts....that's why people use an alias.

  6. #16
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    table 6.2.8(a)
    (3)

    Table 6.2.8 (b)
    (h)

    6.14.1.6 In a lighting circuit, a luminaire may be fed from a socket-outlet on a
    wall (that may be unswitched), provided that the socket-outlet
    a) complies with SANS 164-3 or SANS 164-2-1 (partially dedicated
    socket-outlet), Amdt 1
    b) is protected by earth leakage protection, except in the case where
    SANS 164-2-1 (partially dedicated socket-outlet) socket outlets are fitted,
    Amdt 1

    6.16.3.3.1Stove connections shall be connected by either 6.16.3.3.2 or
    6.6.3.3.3. Amdt 1

    6.16.3.3.3 The stove connections may be wireddirectly between the isolator
    and the stove terminals, by means of a flexible arrangement, which are
    mechanically secured and be terminated on either end. When the stove is
    removed, the final section of hard wiring to the stove terminals has to be
    removed and made safe. Amdt 1

    7.16.3 Voltage drop
    The designer of the distribution system shall select the components in order
    to ensure a minimum voltage drop over the system, which will allow for the
    voltage drop over the entire installation, which is the distribution system, not
    to exceed the 5 % of the circuit nominal voltage (see 6.2.7) and maintaining
    the overall voltage requirements in 5.4.2. Amdt 1
    Comments are based on opinion...not always facts....that's why people use an alias.

  7. #17
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    NOTE 2 In South Africa, it is a statutory requirement that an approved Inspection
    Authority (AIA), or a defined competent person, or a person registered in the
    professional category in terms of the relevant national legislation (see foreword),
    ensures compliance from commencement to commissioning of an electrical installation
    where the intention is to supply five or more users from a new point of supply (see the
    relevant national regulation (see foreword)).
    Amdt 1
    8.1 Inspection and tests
    Section 5 of the test report provides for the person who carried out the
    inspection and testing of the electrical installation as given in 8.5 and 8.6, if
    the results are acceptable, to verify that the installation complies with the
    requirements of this part of SANS 10142.
    NOTE If the test report covers an installation in South Africa that existed before the
    publication of this part of SANS 10142 and extensions or alteractions made since then,
    both blocks that refer to installations which existed before and after the publication of
    this part of SANS 10142 should be marked.
    Amdt 1
    Comments are based on opinion...not always facts....that's why people use an alias.

  8. #18
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    NOTE 1 This calculation gives practical and conservative results. Amdt 1
    NOTE 2 The return current path impedance should be considered where applicable
    Amdt 1

    8.5.2 Complete the inspection table in the test report by confirming the
    statements in item1) to 4) with "Yes" in the appropriate block. "No" answers to
    the following statements will prevent the issuing of the report:
    a) conductors are of the correct rating and current-carrying capacity for the
    protective devices and connected load,
    Pay attention to voltage rating, voltage drop, current-carrying
    capacity and short-circuit capacity.
    b) components have been correctly selected and installed, and are accessible
    where necessary, Amdt 1
    Comments are based on opinion...not always facts....that's why people use an alias.

  9. #19
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    8.6 Testing
    Certain tests shall not be carried out in hazardous locations. Due to the
    characteristics of the intrinsic safety features of equipment, such
    equipment can be damaged by certain tests. Certain tests might be
    impractical in existing installations already under power.
    8.6.1 General
    NOTE Conduct all tests and complete a copy of the test report for each distribution
    board and supply (normal and alternative supplies). Amdt 1
    Comments are based on opinion...not always facts....that's why people use an alias.

  10. #20
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    For the testing of installations that are fully or partially in hazardous or
    specialized locations, see the relevant standards, and complete the additional
    report(s) (see 8.7 for hazardous locations) and the SANS 10142-1-1 test
    report for medical locations. Amdt 1
    Comments are based on opinion...not always facts....that's why people use an alias.

Page 2 of 6 FirstFirst 1234 ... LastLast

Similar Threads

  1. SANS 10142-1 (ed3)
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 23-Apr-21, 06:29 AM
  2. SANS 10142-1:2017 (Ed. 2.00)
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 27
    Last Post: 23-Oct-18, 06:56 AM
  3. SANS 10142 Edition 2
    By Karel Kriel in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 02-Jul-17, 08:20 AM
  4. sans 10142-1:2012
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 23-Apr-13, 05:56 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •