    7.12 Alternative supplies

    Time to sit down put plug in the airpods with background sounds and review section 7.12

    What are the requirements .. .the way I read it.

    Labels labels labels and as many more labels and notices on each DB.

    Indicator - A din mount light next to the main switch is my preference.

    Change over switch as per requirements.

    As per requirements - earth leakage protection for plugs ... I am still trying to understand why people insist on installing earth leakage on the supply to the inverter ... I can understand samll plug in UPS ... but not a 5 kva inverter connected directly to a DB.

    V-O-V type generators not to be connected to the "fixed" electrical installation.
    Comments are based on opinion...not always facts....that's why people use an alias.

  2. #2
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Earthing requirements...

    Where there is no earth spike already installed ... a suitable one must be installed and bonded to the consumer earth terminal with a wire at least half the thickness of the phase conductor ... but not less than 6 mm.

    But this note is rather interesting ... deosnt his mean that if you install a spike you dont need an SPD ... or if you install an SPD you dont need the spike.

    NOTE 2 Protection of photovoltaics can be by means of or surge protective device
    (SPD).

    This section is one that seems to be a little confusing for many.

    7.12.3.1.2 In an installation that is supplied from a combination of
    transformers and alternative supplies located near to each other, the neutral
    points of each of these items shall be connected to a single earthed neutral
    bar (see P.1). This earthed neutral bar shall be the only point at which the
    neutral of the installation is earthed. Any earth leakage device shall be
    positioned in such a way as to avoid incorrect operation due to the existence
    of any parallel neutral/earth path.
    7.12.3.1.3 Where alternative supplies are installed remotely from the
    installation, or from one another, and where it is not possible to make use of
    a single neutral bar or neutral conductor which is earthed, the neutral of each
    unit shall be earthed at the unit and these points shall be bonded to the
    consumer's earth terminal (see 6.12.4). The supply from each unit which
    supplies the installation or part of the installation, shall be switched by means
    of a switch that breaks all live conductors operating substantially together (see
    figures P.2 and P.4), to disconnect the earthed neutral point from the
    installation neutral when the alternative supply is not connected (see also
    6.1.6).
    NOTE Where four pole switching is implemented, consideration should be given to use
    overlapping neutral switching devices.
    7.12.3.1.4 Where only part of an installation is switched to the alternative
    supply in the same distribution board, the neutral bar shall be split (see
    figures P.2 and P.3).
    Comments are based on opinion...not always facts....that's why people use an alias.

  3. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    AC and DC must be mechanically separated and labeled.

    The single line diagram must be displayed at the DB.
    Comments are based on opinion...not always facts....that's why people use an alias.

  4. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,505
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Quote Originally Posted by ians View Post
    Time to sit down put plug in the airpods with background sounds and review section 7.12

    What are the requirements .. .the way I read it.

    Labels labels labels and as many more labels and notices on each DB.

    Indicator - A din mount light next to the main switch is my preference.

    Change over switch as per requirements.

    As per requirements - earth leakage protection for plugs ... I am still trying to understand why people insist on installing earth leakage on the supply to the inverter ... I can understand samll plug in UPS ... but not a 5 kva inverter connected directly to a DB.

    V-O-V type generators not to be connected to the "fixed" electrical installation.
    Another question.

    Why is it not a requirement that a generator have a built in earth leakage ?
    I mean, after all there are socket outlets on a genny where all sorts of appliances are plugged in.

    Derek

  5. #5
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    The use of screw type and not compression type metal conduit ... so no bosal conduit on the roof top ?

    the job I am watching being installed on the roof of a garage ... I wonder if PVC piping and trunking is allowed ... let see as we dig deeper.
    Comments are based on opinion...not always facts....that's why people use an alias.

  6. #6
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Quote Originally Posted by ians View Post
    That an interesting one 5.4.4.6

    The use of screw type and not compression type metal conduit ... so no bosal conduit on the roof top ?

    the job I am watching being installed on the roof of a garage ... I wonder if PVC piping and trunking is allowed ... let see as we dig deeper.
    Is that in Ed 3?

    And then the AC DC mechanically separated is an intresting one as well!

    Sent from my SM-N960F using Tapatalk

  7. #7
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    The last bit is where I get muddled up. It may be a case of someone sitting me down and explaining and then answering all my questions I have to then understand.

    The whole neutral earth bar bit is tricky. I have seen inverters that output need an "earthing box" so as when it kicks in the alt supply the N and E are bonded but when grid is back then it dissconects and the N is now floating... why can it all not be joined to incoming E and then joined to the N to all be the same.??

    I may be missing something very simple but it seems very complex for no reason..

    They say the N and E shall (i think its a shall)be joined on the supplier side only so if that's the case for not perm joining the inveter output N to E I think they must rethink or at least I must be taught why it must be so.



    Sent from my SM-N960F using Tapatalk

  8. #8
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    functional earthing requirements ... this is gonna required more attention ... need to wrap my head around this.
    Comments are based on opinion...not always facts....that's why people use an alias.

  9. #9
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,246
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Quote Originally Posted by Dylboy View Post
    They say the N and E shall (i think its a shall)be joined on the supplier side only so if that's the case for not perm joining the inveter output N to E I think they must rethink or at least I must be taught why it must be so.



    Sent from my SM-N960F using Tapatalk
    Basically ,only the supplier may earth the neutral - You can become the supplier on the load side of a generator or inverter .

    6.1.6 The neutral conductor shall not be connected direct to earth or to the
    earth continuity conductor on the load side of the point of control except as
    allowed in 7.16.4.


    You will see that this is also stipulated in municipal bylaws and Eskom bylaws since the day dot.

    The reason behind the reg is to prevent fires and I will take an extreme case as an example.

    My house is fed from the municipal cable network and I take 80 Amp single phase supply.The neutral is earthed at the substation transformer, 800KVA
    If I then install an inverter and bridge my inverter neutral to earth with a 6sqmm or 4sqmm wire as the inverter is only 1KVA, and that inverter neutral is direct connection to municipal neutral.

    If for some reason the municipal earthed/neutral comes loose or is stolen my house neutral/earth now becomes the earth/neutral for the 800KVA transformer and all imbalanced load will flow through my 16sqmm mains cable and then through my 4sqmm neutral to my inverter which is earthed
    That 4sqmm wire could be in my roof space , overheat due to the current flow and cause a fire .
    That earth neutral current flow could be as high as 200Amp on an imbalanced load.

    That is the though process for that particular regulation

  10. Thanks given for this post:

    Dylboy (04-Dec-21)

  11. #10
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    Quote Originally Posted by GCE View Post
    Basically ,only the supplier may earth the neutral - You can become the supplier on the load side of a generator or inverter .

    6.1.6 The neutral conductor shall not be connected direct to earth or to the
    earth continuity conductor on the load side of the point of control except as
    allowed in 7.16.4.


    You will see that this is also stipulated in municipal bylaws and Eskom bylaws since the day dot.

    The reason behind the reg is to prevent fires and I will take an extreme case as an example.

    My house is fed from the municipal cable network and I take 80 Amp single phase supply.The neutral is earthed at the substation transformer, 800KVA
    If I then install an inverter and bridge my inverter neutral to earth with a 6sqmm or 4sqmm wire as the inverter is only 1KVA, and that inverter neutral is direct connection to municipal neutral.

    If for some reason the municipal earthed/neutral comes loose or is stolen my house neutral/earth now becomes the earth/neutral for the 800KVA transformer and all imbalanced load will flow through my 16sqmm mains cable and then through my 4sqmm neutral to my inverter which is earthed
    That 4sqmm wire could be in my roof space , overheat due to the current flow and cause a fire .
    That earth neutral current flow could be as high as 200Amp on an imbalanced load.

    That is the though process for that particular regulation
    That makes all the sense! Thank you for taking the time to explain! I should have thought of the PEN fault. I really appreciate it !

    Sent from my SM-N960F using Tapatalk

Page 1 of 4 123 ... LastLast

Similar Threads

  1. Fuel supplies.
    By JohnW1234 in forum South African Politics Forum
    Replies: 6
    Last Post: 23-Dec-21, 10:45 AM
  2. COC including supplies from UPS
    By RegElec in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 11-Nov-21, 06:26 AM
  3. alternate supplies
    By ians in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 31-Jul-20, 12:29 PM
  4. Multiple supplies in one building
    By ians in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 24-Jul-19, 11:50 AM
  5. KA testing on UPS Supplies
    By RegElec in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 22-Jul-14, 06:33 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •