    Separation of AC and DC wiring in backup systems

    It seems there are rules with regards to AC and DC separation ... it seems the attitude is the same as my attitude to euro plugs in my house.

    What are the facts with regards to installing AC and Dc wiring for backup systems ... in the same wireways ...

    is there a specific distance

    types of barriers required

    crossing over of AC and DC wires in wireways.

    What happens when you get to the inverter and you have a whole lots of AC and DC wires you need to now get into the inverter?
    Comments are based on opinion...not always facts....that's why people use an alias.

  2. Thanks given for this post:

    Dylboy (26-Nov-21)

  3. #2
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    I have the exact same thoughts! It irritates me to no end! We need the definition of separation.

    Is a single layer of PVC considered suitable separation... is it a 5mm gap... is it a PVC trunking plastic thickness fine like in those Dual power trunkings...

    What about if they cross wires at 90° or run parallel....


    What about having some 12V DC relays in a AC DB board... how far apart must they be to AC breakers, can the wires touch or just there be a 10mm gap or mist DC be 100% jn its own enclosure...? Smaft home stuff is real and there is DC components that will control AC so we need clarification.

    There may be some somewhere but I can't find it yet


    Sent from my SM-N960F using Tapatalk

  4. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,247
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    I find the regulation clear with regards to separation
    We tend to run a U shape trunking when it comes to inverters and DC cabling and use a split trunking if need be .
    We have also run cable tray with a P8000 in the tray for Data cables to keep separate

    Have attached reg below that I feel is relevant and a pic of the latest install.



    6.1.7 If conductors that operate at different voltages run in the same wireway,
    the insulation of each conductor shall be able to withstand the highest
    conductor voltage in the wireway. Alternatively, the conductors shall be
    separated by a continuous barrier of insulating material or earthed metal.

    6.1.10 Conductors that form part of a d.c. installation shall not be run in the
    same wireway as conductors that form part of an a.c. installation.

    3.85
    wireway
    open or enclosed route or support such as a rack, tray, ladder, ducting,
    trunking, sleeving or conduit that is intended to contain conductors or cables
    NOTE A wireway can consist of one or more separate wireway channels, each of
    which is intended for different services such as installation wiring and
    telecommunication wiring.



    Click image for larger version. 

Name:	1.jpg 
Views:	323 
Size:	23.6 KB 
ID:	8407

  5. Thanks given for this post:

    Dylboy (29-Nov-21)

  6. #4
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    That is well and good for wireways but I am more asking about in a DB, apologies i was not specific but that is more where my mind is.


    Sent from my SM-N960F using Tapatalk

  7. #5
    Junior Member
    Join Date
    Oct 2018
    Location
    Gauteng
    Posts
    19
    Thanks
    2
    Thanked 2 Times in 2 Posts
    Hi,

    I think GCE covered it all pretty nicely from a regs point of view for wireways

    For me the remainder is down to good practice and best effort. Wherever possible run AC and DC wires separately. Where paths cross ... try cross at 90 degrees.

    In some panels/DB's it is virtually impossible ... but perhaps a strategically placed piece of trunking / tubing can help separate some of the "delicate" wires.

  8. #6
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    When you run the P8000 ... do you put short pieces of earth wire with a lug or do you just use the pop rivetted joiner for the P8000 as the earth continuity.
    Comments are based on opinion...not always facts....that's why people use an alias.

  9. #7
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by BobZA View Post
    Hi,

    I think GCE covered it all pretty nicely from a regs point of view for wireways

    For me the remainder is down to good practice and best effort. Wherever possible run AC and DC wires separately. Where paths cross ... try cross at 90 degrees.

    In some panels/DB's it is virtually impossible ... but perhaps a strategically placed piece of trunking / tubing can help separate some of the "delicate" wires.
    The 90 % cross over is more for data applications ... when it comes to AC/DC and voltage variations ... its more about the highest voltage insulation protection.
    Comments are based on opinion...not always facts....that's why people use an alias.

  10. #8
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,247
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Quote Originally Posted by ians View Post
    When you run the P8000 ... do you put short pieces of earth wire with a lug or do you just use the pop rivetted joiner for the P8000 as the earth continuity.
    use the pop rivet or tek screw for bonding and if not joined to the DB then an earth at the beginning
    I have never seen any consultant insist on a bonding strap on each piece besides Transnet

  11. #9
    Email problem Weable's Avatar
    Join Date
    Nov 2021
    Location
    Ballito
    Posts
    9
    Thanks
    2
    Thanked 0 Times in 0 Posts
    GCE covered the answer perfectly. I would not recommend to any one at all to ever run DC and AC in the same wire ways. Always keep them separated and clearly marked. If in the same enclosure be it trunking or DB and if there had to be a problem and these currents mingle together for an evening drink. It will be a totally off the chat show

  12. #10
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,247
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Quote Originally Posted by Dylboy View Post
    That is well and good for wireways but I am more asking about in a DB, apologies i was not specific but that is more where my mind is.


    Sent from my SM-N960F using Tapatalk
    Been thinking on this one and specifically to home automation type systems .

    Technically a DB is not a wireway .
    The home auto system use extremely low DC and generally with low current limiting capabilities to prevent damage to the components.
    The home automation relays would generally be built into there own separate enclosure and I would term the "DB" as a motor control center or machine

    I would say " each conductor shall be able to withstand the highest conductor voltage" as per 6.1.7 and as mentioned above , keep the control wiring in a separate trunking within the DB.
    I would also use clause 5.1 note 2

    5 Fundamental requirements
    5.1 General
    All commodities in an electrical installation shall be installed in accordance
    with the requirements in this part of SANS 10142 and with the manufacturer's
    instructions, where applicable.
    NOTE 1 This clause contains the general safety principles applicable to electrical
    installations.
    NOTE 2 The manufacturer's instructions may contain more stringent requirements.


    To me the regulations are written around DC wiring having a high short circuit ratings and the prevention of arching like experienced on PV , inverters ,Battery banks and telecommunication equipment.
    I cannot think of anywhere that home automation systems would be mentioned in SANS 10142-1

Page 1 of 2 12 LastLast

Similar Threads

  1. [Question] Backup error
    By Michellevn in forum Accounting Forum
    Replies: 2
    Last Post: 20-Apr-20, 08:47 AM
  2. Hobby wiring: Wiring requirements for a DCC railway layout
    By icrob in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 23-Jul-16, 05:29 PM
  3. Backup to ADSL
    By IanF in forum Technology Forum
    Replies: 9
    Last Post: 27-Jan-11, 02:46 PM
  4. Separation of powers?
    By duncan drennan in forum South African Politics Forum
    Replies: 3
    Last Post: 11-Oct-07, 09:17 PM
  5. The Tao of Backup
    By duncan drennan in forum Technology Forum
    Replies: 1
    Last Post: 10-Sep-06, 11:12 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •