Thread: Waco IP 67 Sockets

  1. #1
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts

    Waco IP 67 Sockets

    Hi

    Anyone else had trouble with Waco IP 67 sockets. Used a load of 16 amp 5 pin in a dry food mixing factory and out of 8, 3 keep flooding.

    Conduit was top entry but is threaded so adapted screwed and glued (as well as the conduit) plus a little silicon for good measure.

    The box is sealed in that no fixings penatrate the inner part of the isolator.

    If it was just one I'd be ok, maybe one failed but 3? Are they just not very good?

    Just me or is it "a thing"

    Thanks

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,487
    Thanks
    137
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Maybe the O ring seal is missing on the lid?
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. #3
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts
    Quote Originally Posted by Justloadit View Post
    Maybe the O ring seal is missing on the lid?
    Its there and looks like its sitting nice. I wondered if it was getting some how by the rotary switch.

    The switches get covered in flour and dough so they do hose them down but IP 67v should be good for that?

  4. #4
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,487
    Thanks
    137
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Maybe through thw switch mechanism, but then there should be evidence of water on the switch.
    Also check how the enclosure is affixed against the wall.
    Can water run down the wall and travel along the screw inside the box?
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

Similar Threads

  1. NOVA and DIN sockets
    By RegElec in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 12-Dec-19, 10:04 PM
  2. New sockets - sans 164-2
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 30
    Last Post: 26-Apr-19, 09:39 PM
  3. Unswitch sockets ok?
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 28-Nov-16, 12:34 PM
  4. crabtree plug sockets
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 05-Aug-12, 10:10 PM
  5. atx sockets
    By bergie in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 10-Apr-12, 12:56 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •