    Can anyone explain what the current ratings AC1 and AC3 actually mean in the attached brochure.

    Thanks in advance ... Derek

    https://www.l-osales.co.za/download-...ol-gear-s1.pdf


    Edit: Found the explanation.

    Next question. If one uses a 3 phase contactor to switch a single phase live connected in parallel through the 3 contacts, can it be assumed that the total load current will be shared equally through the 3 contacts ?
    Last edited by Derlyn; 23-Nov-21 at 09:24 AM.

  2. #2
    Gold Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    530
    Thanks
    12
    Thanked 130 Times in 109 Posts
    Quote Originally Posted by Derlyn View Post

    Next question. If one uses a 3 phase contactor to switch a single phase live connected in parallel through the 3 contacts, can it be assumed that the total load current will be shared equally through the 3 contacts ?
    You can assume that it will be shared equally - Don't size to tight rather go one size up

  3. #3
    Gold Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    565
    Thanks
    29
    Thanked 59 Times in 57 Posts
    Thanks GCE.
    Trying to use the smallest contactor possible for house supply. Big difference in price between a 65A and 35A contactor.

    I think I will go for about 30A. That should do it for a 63 Amp main breaker.

    Once again, thanks.
    Much appreciated.
    Derek.

  4. #4
    Gold Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    565
    Thanks
    29
    Thanked 59 Times in 57 Posts
    This little project is not as simple as it seems. Trying it on my own house before offering it to any clients, of which there are many, waiting in anticcipation.

    The idea is to use a fridge safe and a contactor to delay the power resumption after loadshedding.

    Theoretically the supply will go through the main switch then through the contactor and supply the installation.

    Problem is that the fridge safe plugs into a plug. I will have to install a plug fed from above the contactor through a circuit breaker. Now, the problem is that this plug won't be on earth leakage so I have to install a seperate earth leakage just for this monitoring plug. Gets more complicated as one progresses.

    Derek

  5. #5
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,874
    Thanks
    566
    Thanked 924 Times in 746 Posts
    AC1 and AC3 refer to the type of load connected ie how capacitive or inductive is it. A normal heating element for example has a unity power factor (PF = 1) and would be classed as an AC1 load. A motor is an inductive load, it might have a power factor of 0.7 for example and it would be classed as an AC3 load.

    Because an inductive load causes a phase angle between the voltage and the current it causes more damage to switch contacts when it's turned on and off. In the old days we just used a derating figure of 50% if it was an inductive load but nowadays switches, relays and contactors often come with different current ratings specified for AC1, AC3 and even AC4 class loads. The AC3 current a contactor can handle will always be significantly less than the AC1 current. Sometimes the manufacture just derates the lifespan of the device ie it may be good for 60000 operations with an AC1 load or 10000 operations with an AC3 load.

    This is an old ducument but there's a full list of the load classifications on page 2.

    iec_contactors.pdf
    _______________________________________________

    _______________________________________________

  6. Thank given for this post:

    adrianh (24-Nov-21), Dave A (25-Nov-21), Derlyn (25-Nov-21)

Similar Threads

  1. [Question] Pottery Kiln Contactor Replacement
    By debtcollectorZA in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 29-Aug-21, 06:58 PM
  2. kA ratings
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 22
    Last Post: 21-Jan-19, 06:34 AM
  3. Contactor Question
    By Gei in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 24-Jun-11, 10:27 PM
  4. Listener AR ratings - how they work?
    By garthu in forum Marketing Forum
    Replies: 1
    Last Post: 29-Aug-10, 10:23 PM
  5. Downrated credit ratings - how will this affect us?
    By Dave A in forum Business Finance Forum
    Replies: 1
    Last Post: 13-Nov-08, 08:13 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •