    Angry earth leakage trip on 30mA

    Good day all
    I have a house on a farm that consists of 4 shipping containers that needs a COC.
    The power supply is from a PV system and the neutral and earth is bonded on the inverter side. There is no Escom feed to the house. The four containers are earthed to each other and the DB with 16mm sq bare copper. The house have no earth to the ground at the moment, we plan on connecting two earth mats to the building, on opposite corners of the house

    My problem is the earth leakage that only trips on 30mA when testing the electricity. :-(
    Any suggestions on how to fix it or do I COC it like that?

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,484
    Thanks
    104
    Thanked 141 Times in 134 Posts
    Quote Originally Posted by Thys LOW Elektries View Post
    Good day all
    I have a house on a farm that consists of 4 shipping containers that needs a COC.
    The power supply is from a PV system and the neutral and earth is bonded on the inverter side. There is no Escom feed to the house. The four containers are earthed to each other and the DB with 16mm sq bare copper. The house have no earth to the ground at the moment, we plan on connecting two earth mats to the building, on opposite corners of the house

    My problem is the earth leakage that only trips on 30mA when testing the electricity. :-(
    Any suggestions on how to fix it or do I COC it like that?
    Hello brother

    As far as I know, if the residual current rating of the ELR is 30mA then passing a 30 mA current from phase to earth, the ELR must trip.
    For the same ELR unit, passing a 50% current from phase to earth ie. 15mA, the ELR should not trip.

    So tripping on 30mA is a pass. See 8.6.12.

    Peace out ... Derek

  3. #3
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    224
    Thanks
    11
    Thanked 21 Times in 19 Posts
    Thanks Derek

    For some unknown reason I was under the impression that the ELR must trip before 30mA. I did a bit of reading, consult old training manuals and found tht 30 mA is high but acceptable and passable.

    Thanks for your response

    Greatings Thys

Similar Threads

  1. Earth Leakage
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 10-May-16, 10:11 PM
  2. [Article] Earth leakage unit problems (trip) after solar installation
    By Dries in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 09-Sep-15, 04:13 PM
  3. earth leakage trip due to lightning
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 19-Dec-14, 07:33 PM
  4. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM
  5. Earth leakage trip 7 min past the hour every hour
    By IMHO in forum Electrical Contracting Industry Forum
    Replies: 39
    Last Post: 09-Jan-13, 07:13 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •