    Pottery Kiln Contactor Replacement

    Hi Guys,

    My wife's pottery kiln is not longer heating up.
    Using a clamp meter I ascertained it is not drawing much current as this thing eats electricity and drawing almost 30amp on a single phase when operational.
    On further inspection I found than the neutral wire coming from a 24Amp contactor has burned off completely. The contactor is also badly burnt but still clicks.
    I am not sure if the under spec'd contactor was the source of the problem or if the wires are a little thin for the current they are supposed to carry.
    The palooka who wired this thing ran a single neutral wire to the elements and 2 live wires, so obviously the neutral wire has to carry double the current.
    I suspect this was done to convert it from 3 phase to 1 single phase.

    Click image for larger version. 

Name:	Riken RAB12T10 2.jpeg 
Views:	214 
Size:	67.5 KB 
ID:	8255

    Click image for larger version. 

Name:	Burned Wires.jpg 
Views:	209 
Size:	39.2 KB 
ID:	8256

    The contactor is no longer in production as I need and equivalent but perhaps a little beefier.
    In my personal experience the sales people at ACDC and Communica are nothing more than admin clerks with very little knowledge on the stuff they sell.
    If you give them the item number they know where to find it in the store room, but they aren't there to give you advise.

    Can someone point me to a drop in replacement for this contactor and where best to buy this from.

    Thanks
    Theo

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,488
    Thanks
    137
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    That contactor is rated for a 3KW motor at 230V, which is around 6Amps. The contactor may say 25A continuous, but that is debatable.
    You can go to Mantech or any other electrical wholesaler and get a contactor rated at 32A.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    The type of damage visible in the bottom photo is almost always caused by a poor termination. Maybe the wire became loose in the terminal clamp over time. Loose connections mean lot of heat and eventual failure (sometimes causing fire). As per Justloadit, the nature of the load is linear (good power factor) and the form factor of the contactor is standard so any 3-pole contactor with an AC1 rating 25 Amps or above that has a normally open auxilliary contact and a similar voltage coil should be a suitable replacement.
    _______________________________________________

    _______________________________________________

  4. #4
    Junior Member
    Join Date
    Jun 2014
    Location
    South Africa
    Posts
    14
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Thanks for all the help. I ended up rewiring the whole kiln and replaced the burned contactor with a suitable replacement unit. So far so good. I will only know for sure once the kiln has gone through a full 8 hour firing cycle. I am confident though.

Similar Threads

  1. Problem with industrial geyser tank contactor
    By BlueArc in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 19-Dec-13, 08:51 PM
  2. Laser printer replacement
    By ians in forum General Chat Forum
    Replies: 1
    Last Post: 18-Sep-12, 02:38 PM
  3. Unnecessary carb replacement
    By Paterkie in forum Consumer Protection Act Forum
    Replies: 7
    Last Post: 05-May-12, 09:28 AM
  4. Oven Element Replacement
    By rfnel in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 29-Jun-11, 11:08 AM
  5. Contactor Question
    By Gei in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 24-Jun-11, 10:27 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •