Hi Guys,
My wife's pottery kiln is not longer heating up.
Using a clamp meter I ascertained it is not drawing much current as this thing eats electricity and drawing almost 30amp on a single phase when operational.
On further inspection I found than the neutral wire coming from a 24Amp contactor has burned off completely. The contactor is also badly burnt but still clicks.
I am not sure if the under spec'd contactor was the source of the problem or if the wires are a little thin for the current they are supposed to carry.
The palooka who wired this thing ran a single neutral wire to the elements and 2 live wires, so obviously the neutral wire has to carry double the current.
I suspect this was done to convert it from 3 phase to 1 single phase.
The contactor is no longer in production as I need and equivalent but perhaps a little beefier.
In my personal experience the sales people at ACDC and Communica are nothing more than admin clerks with very little knowledge on the stuff they sell.
If you give them the item number they know where to find it in the store room, but they aren't there to give you advise.
Can someone point me to a drop in replacement for this contactor and where best to buy this from.
Thanks
Theo