    Twin and earth stripped.

    Hi all
    Is it legal to strip twin and earth and use the conductors on their own without the outer covering if it is in conduit ?

    Peace out .. Derek

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,247
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    I don't see any reason why not if it is in a conduit and the regulations allow for solid strand as long as it does not exceed 2,5sqmm- Pasted what I see as the relevant regulation
    Would be an expensive and time consuming way of getting single wire


    6.3.2 Construction
    6.3.2.1 Conductors of nominal cross-sectional area exceeding 2,5 mm2 shall
    be stranded, except in the following cases, where solid conductors may be
    used:
    a) conductors of mineral-insulated metal-sheathed cables;
    b) internal connections of distribution boards, switchgear and industrial
    controlgear;
    c) busbars;
    d) aerial conductors;
    e) aluminium conductors of nominal cross-sectional area 16 mm2 or more;
    and
    f) copper conductors of nominal cross-sectional area 16 mm2 or less that are
    used in multicore cables.

  3. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,511
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Thank you, brother.
    Busy with a house rewire. Have bought T&E for the job but there is one short conduit run where we are struggling to get T&E to co- operate, so I thought of stripping them to solve the problem, seeing that the wire has been purchased for this job. Just wasn't sure about the legality.

    Thanks once again, brother.
    Much appreciated.

    Peace out .. Derek.

Similar Threads

  1. Twin+E stripper
    By ians in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 30-Dec-20, 07:43 AM
  2. [Question] Twin+E exposed to the sun
    By ians in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 23-Dec-19, 07:23 AM
  3. [Question] Twin-earth cable sheathing removed
    By Ishmaelmo in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 07-Jun-19, 08:39 AM
  4. Twin and earth connections .
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 23-Feb-18, 08:59 PM
  5. twin and earth question
    By Hotspot in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 20-Jun-16, 10:10 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •