    Oven tripping earth leakage

    Hi,

    My oven is tripping the earth leakage only under a certain condition.

    The oven has a combo (grill & top) element and a bottom element. The oven has 4 settings, i.e. grill, top, bottom and top & bottom. When each of the 3 elements are switched on individually, i.e. grill, top and then bottom, the earth leakage does not trip. When the top and bottom elements are switched on together then the earth leakage trips after about 2 minutes. I checked the top and bottom elements for cracks/holes but there were none.

    Any idea what could be causing this behaviour?

    Thanks in advance!

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,247
    Thanks
    34
    Thanked 304 Times in 258 Posts
    All elements have a slight leak to earth - Each element individually does not have " sufficient " leakage to cause the earth leakage to trip but the 2 together may push the leakage to above the 30ma that will cause the earth leakage to trip .

    If you left the one element on for 30 min , switch off and then leave the other one on for 30 min it will more than likely "dry " the element out and both will work together.

    A stove does not have to be on earth leakage if it is connected up as a stove point- If it is plugged into a socket then the socket has to be on earth leakage .

  3. #3
    Bronze Member
    Join Date
    Mar 2012
    Location
    Account_Deleted
    Posts
    165
    Thanks
    122
    Thanked 23 Times in 18 Posts
    Hi all, where does the regs stand regarding the use of the stove coupler.

    https://ecasa.co.za/technical/connec...e-regulations/

  4. #4
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,659
    Thanks
    3,307
    Thanked 2,678 Times in 2,259 Posts
    Blog Entries
    12
    Quote Originally Posted by ACEsterhuizen View Post
    Hi all, where does the regs stand regarding the use of the stove coupler.

    https://ecasa.co.za/technical/connec...e-regulations/
    Due to this regulation (6.16.3.3) connection to free-standing stoves could place the contractors’ credibility at risk. This regulation needs reconsideration from the SABS 10142-1 working group due t the fact that these parts are difficult to source, making them impractical in today’s installations. The installation of these devices created complications in installations that should not exist. In short, this concern should be raised and taken forward.
    It would be good to see some feedback from the Technical Committee on this!

  5. Thanks given for this post:

    ACEsterhuizen (19-May-21)

  6. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,247
    Thanks
    34
    Thanked 304 Times in 258 Posts
    The procast stove couplers are readily available again and being made by Jac Manufacturing ( www.jacman.co.za )

    With that said there has been a publication to amend the type of socket that can be used for stoves - It is out for public comment at the moment
    Attached Files Attached Files

  7. Thank given for this post:

    ACEsterhuizen (19-May-21), AndyD (11-May-21), Dave A (09-May-21)

  8. #6
    New Member
    Join Date
    May 2021
    Location
    Johannesburg
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by GCE View Post
    If you left the one element on for 30 min , switch off and then leave the other one on for 30 min it will more than likely "dry " the element out and both will work together.
    Thank you! Will give it a try.

  9. #7
    New Member
    Join Date
    May 2021
    Location
    Victoria, Florida, USA
    Posts
    1
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Hi....genuine approach to check is with a taps analyzer. I surmise a megger would work effectively as well. There probably won't be sufficient current from a computerized multimeter to see the break . its sounds clearly an awful one in any case . one quite safe approach to test would be eliminate the wires going to it and protect them at that point turn it on.

Similar Threads

  1. Earth Leakage Breaker (RCD) Tripping
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 14-Jul-23, 02:53 PM
  2. Ceiling fan tripping earth leakage.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 04-Feb-21, 09:04 AM
  3. Low earth leakage tripping current
    By SeanM in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 15-Mar-19, 07:19 PM
  4. earth leakage tripping issue
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 16-Jan-19, 12:13 PM
  5. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •