    MV and LV Cables in Substation

    Good day all,

    I have a contractor who is busy with a new installation of MV cables in a substation (11kV).
    From experience I know that MV and LV cables are not supposed to be mixed and normally run separate from each other.
    However I cannot seem to find the standards which supports this, can any body maybe point me in the right direction as to where I can find the appropriate standards for substation installations?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,246
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    I know of these 2 regulations that guide you towards the separation of voltages - Not sure if that is what you are looking for

    From Sans 10142-1
    6.1.7 If conductors that operate at different voltages run in the same wireway,
    the insulation of each conductor shall be able to withstand the highest
    conductor voltage in the wireway. Alternatively, the conductors shall be
    separated by a continuous barrier of insulating material or earthed metal.



    From Sans 10142-2
    5.4 Buildings and enclosures
    5.4.1 Buildings shall comply with national building codes (SANS 10400-T) and fire regulations.
    Amdt 1; amdt 2
    5.4.2 Substation buildings shall comply with the requirements of the Electrical Machinery
    Regulations
    (see foreword). Amdt 1
    5.4.3 No exposed liquid, gas or effluent pipes with operational or service openings shall be
    installed inside substation buildings.
    5.4.4 A barrier shall separate the MV and LV equipment that are installed in the same building.
    The MV bushing connections shall be sealed and insulated.
    5.4.5 Notwithstanding the ventilation provided, rooms that contain open type lead batteries shall be
    considered as locations with corrosive environments. Walls, ceilings and floors shall comply with the
    requirements for protection against corrosion and gaseous products. Means shall be provided to
    prevent corrosive substances from entering any drainage systems (see also the requirements for
    hazardous locations in SANS 10108).

Similar Threads

  1. [Question] flexible cables
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 18
    Last Post: 11-Sep-23, 07:52 AM
  2. Too many cables in conduit
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 31
    Last Post: 12-Mar-19, 09:02 AM
  3. VLF Test on xlpe cables
    By Eskom in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 20-Feb-16, 08:37 AM
  4. Supply cables
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 17-Aug-13, 08:40 AM
  5. Does anyone know where I can find these cables?
    By tec0 in forum Technology Forum
    Replies: 2
    Last Post: 29-May-12, 04:47 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •