    Earth continuity conductors

    How many of you still install earth conductors as we have in the old days?

    I have been spending time reading the SANS book to find ways to cut costs.

    6.12.1.1 An earth continuity conductor

    Do you install a 6 mm wire if you run a red and black 6mm or do you use a 4 mm wire.

    If you look at table 6.28 ... protective device 40 amp ... so long as the cable is not longer than 80 m a 4 mm earth wire is fine.

    If you look at twin+e or armoured cable ... those little earth conductors used are a fraction of the size in comparison to the live conductors.
    Comments are based on opinion...not always facts....that's why people use an alias.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi Ians

    I assume you looking at ED2 of Sans table 6.28 - Ed 3 is a whole lot different but there are other factors that come into play.
    In Ed 3 the distance for 4sqmm earth is now 40m depending on external factors - It is no longer as str forward as sizing the earth one size down on the phase conductor and not really using greater than 70sqmm BCEW

    We generally use ECC cable which has a different set of dynamics and the fault current path is calculated by the manufacturer and takes into account surface area to dissipate the heat on a fault current besides the thickness of the copper.
    I am assuming that it is similar with T&E and surfix and that the earth being used is calculated based on the max current that can be drawn on the length of surfix you use.

    With single cores it changes

  3. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Too late its already installed this morning ... if it was safe enough for ed 2 ... I am sure it will be fine ... It seems I am going to have to purchase ed 3 ... anyone know if there are any changes ... upgrades or modification in the next few months ... I dont want to go waste money buying ANOTHER BOOK to add to my already full shelf of SANS books?
    Comments are based on opinion...not always facts....that's why people use an alias.

  4. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Quote Originally Posted by ians View Post
    ... anyone know if there are any changes ... upgrades or modification in the next few months ...?
    How long is a piece of string ?

    Have not heard anything that is changing shortly - Ed 2 was valid for 3 years - We not quite into the first year of ED3 yet so hopefully still 2 and a bit to go.

Similar Threads

  1. no earth conductors in home installation
    By markthespark in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 30-May-19, 09:27 AM
  2. Foundation earth
    By Lourie1251 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 27-Nov-17, 07:41 PM
  3. [Question] Using 1 core as an earth?
    By Chilli in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 21-Aug-17, 11:01 PM
  4. Bank Account Continuity
    By pete9999 in forum Accounting Forum
    Replies: 7
    Last Post: 29-Jun-17, 08:00 PM
  5. [Question] electrical earth continuity
    By Groen Karoo in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 14-Sep-11, 08:07 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •