    How to insulate a ferrule

    Hi

    I'm currently modifying a db and are required to extend some of the wires in the dB. I suppose bare solid copper ferrules will be the best option for the joints. What are the best option for insulation? A few twists of nitto tape or heatsshrink? Also are there any rules for the overlapping of the joint insulation?

  2. #2
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    The old fashion way to do it would be to use a ferrule (the right size) ...rubber tape then nitto tape ... the problem with using tape ... it gets gooooey ... you can use heat shrink ... just not sure of the rating for some of the crap sold to the industry ... it might pay to double layer or just buy a good brand like 3M.

    I am busy upgrading a couple of DB's ... I am using 3 tier boards and installing din rail terminals blocks to terminate the short cables and where I cant fit terminal blocks ... I secure a Wago 221 mounting carriers to the side of the DB and clipping the 2/3 or 5 way 221 wago connectors ... quick and easy ... expensive but neat andsaves time.
    Comments are based on opinion...not always facts....that's why people use an alias.

  3. Thanks given for this post:

    Frans400 (07-Mar-21)

  4. #3
    Full Member
    Join Date
    Nov 2019
    Location
    Sa
    Posts
    32
    Thanks
    6
    Thanked 2 Times in 2 Posts
    Thank Ian, 221 it is then.

  5. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Wagos are a great option. With ferrules I use 2 layers of adhesive lined heat shrink but obviously this has to be slid onto the wire before crimping. For an existing ferrule you could use self-amalgamating tape but usually I'd just cut it off and re-ferrule with heat shrink.
    _______________________________________________

    _______________________________________________

Similar Threads

  1. Ferrule compliance
    By Gnome in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 15-May-18, 06:32 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •