    Neutral impedance

    Good afternoon.
    Can somebody please explain the new COC document with relation to neutral loop impedance and how are we to test for it??
    I know how to test for the Earth loop impedance using the T1825 meter, but how do we test for neutral impedance?? Please help.
    Thanking you kindly

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    PEFC test will give you earth loop impedance, PSCC test will give you neutral loop impedance. On a TN-C-S or PME'd supply these test results should give identical results.
    _______________________________________________

    _______________________________________________

  3. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,484
    Thanks
    104
    Thanked 141 Times in 134 Posts
    Brother

    What I do, using the same impedance tester as you, is to swap the earth and neutral leads. ie. connect the black lead to earth and the green lead to neutral.

    You will then be doing a neutral impedance test, but as Andy said .... The readings should be identical.

    Maybe some of the other toppies can comment.

    Peace out ... Derek

  4. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Came across 1 - New-Neutral-Loop-Impedance-Test-SANS-10142-1-Ed-3.pdf this article this morning and remembered the thread on Neutral impedance

    NOTE 1 For this test using the same instrument as per 8.6.5.1, both the
    neutral and earth clamps of the instrument will be connected onto the
    neutral conductor

  5. Thanks given for this post:

    Dave A (20-Apr-21)

  6. #5
    Full Member
    Join Date
    Jul 2018
    Location
    Brits
    Posts
    28
    Thanks
    10
    Thanked 1 Time in 1 Post
    Quote Originally Posted by GCE View Post
    Came across 1 - New-Neutral-Loop-Impedance-Test-SANS-10142-1-Ed-3.pdf this article this morning and remembered the thread on Neutral impedance

    NOTE 1 For this test using the same instrument as per 8.6.5.1, both the
    neutral and earth clamps of the instrument will be connected onto the
    neutral conductor
    thats correct!Also have it like that did unit standards early this year where they also instrcuted us to do it in that manner.

  7. #6
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    OR just buy a decent meter like a fluke 1654 ?
    Comments are based on opinion...not always facts....that's why people use an alias.

  8. #7
    Full Member
    Join Date
    Jul 2018
    Location
    Brits
    Posts
    28
    Thanks
    10
    Thanked 1 Time in 1 Post
    Quote Originally Posted by ians View Post
    OR just buy a decent meter like a fluke 1654 ?
    It has been discontinued!Great meter worked with 1 few months ago!

  9. #8
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,484
    Thanks
    104
    Thanked 141 Times in 134 Posts
    I remember the thread on neutral impedance where I advised someone to swop the earth and neutral leads to get the neutral loop impedance.

    I was wrong.

    Please accept my humble apologies.

    Connecting both the earth and neutral leads to the neutral is of course the correct method.

    Peace out .. Derekk

  10. #9
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Yip us old people who look after our equipment ...dont keep up to date with the latest trends ... there is already a 1664 FC ... at only R482000.00 ... trying to justify that kind of outlay doing COC's at R600 could be a challenge

    https://www.fluke.com/en-gb/product/.../fluke-1664-fc
    Comments are based on opinion...not always facts....that's why people use an alias.

  11. #10
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,484
    Thanks
    104
    Thanked 141 Times in 134 Posts
    Ian. I still have an AVO meter that gets used regularly.

    I also prefer an old analogue megger. Needle to the left .. good. Needle to the right .. bad.😆

Page 1 of 2 12 LastLast

Similar Threads

  1. [Question] Loop Impedance
    By C-Cam in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 20-Jan-21, 03:00 PM
  2. Earth loop impedance testing
    By ians in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 24-Jan-19, 09:34 AM
  3. high loop impedance reading
    By ians in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 20-May-15, 07:00 PM
  4. [Question] Earth Loop Impedance on COC test.
    By Jasond MIE in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 06-Mar-15, 01:42 PM
  5. Help me ! input impedance of field effect transistor
    By mattmro444 in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 09-Aug-14, 08:33 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •