    Geyser Replacement Tripping Earth Leakage - Assistance Please

    Hello,

    Need some assistance please,

    Had a new geyser installed at my dads place - very old house and electrical installation.

    The geyser that was replaced was not used for a few years and the piping (old iron type) started to leak in the ceiling so we decided to put a new one in.

    So...

    New geyser installed and old geyser wiring extended to new geyser as its in a different location with new piping.

    The new geyser has power on it with the earth leakage off / down...
    So we put the geyser CB off and put the earth leakage on... Everything works fine...
    The moment we switch the geyser on it trips the earth leakage...

    Additional Info
    3 phase power
    Very old DB and possibly wiring standards with the double thickness CBs compared to new ones
    Old geyser is still in ceiling just fully disconnected and drained now
    The house does have an additional completely new geyser installation from a few years back that is working perfectly fine.


    Any suggestions welcome, thanks in advance...

    Installers only suggestion is that the earth leakage is bypassed and the geyser does not have a proper earth (they connected to the existing earth from the old geyser)
    They also tried disconnecting the earth in the geyser terminal block on the side with same result.

  2. #2
    Bronze Member
    Join Date
    Mar 2018
    Location
    Western Cape
    Posts
    120
    Thanks
    11
    Thanked 15 Times in 14 Posts
    Greetings

    Sounds like to neutral of the geyser is on the earth leakage neutral bar and to live of the geyser is not fed from earth leakage.

  3. Thanks given for this post:

    AmithS (02-Feb-21)

  4. #3
    Junior Member
    Join Date
    Jun 2020
    Location
    Jhb
    Posts
    14
    Thanks
    0
    Thanked 6 Times in 4 Posts
    Quote Originally Posted by SeanM View Post
    Greetings

    Sounds like to neutral of the geyser is on the earth leakage neutral bar and to live of the geyser is not fed from earth leakage.
    Yes I agree.

    Check where the Geyser Neutral is from.

    From what you describe the neutral was connected from a point upstream of the Earth Leakage . It should be downstream from the EL.
    SANS10142 does state that warm water heaters/geyser must be protected by an EL device.

  5. Thanks given for this post:

    AmithS (02-Feb-21)

  6. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by AmithS View Post
    ...........Installers only suggestion is that the earth leakage is bypassed and the geyser does not have a proper earth (they connected to the existing earth from the old geyser)
    They also tried disconnecting the earth in the geyser terminal block on the side with same result.
    Disconnecting the earth on a geyser won't stop an earth leakage tripping, there are parallel paths to earth via pipework, bonding straps and even the water in the pipes....and plumbers shouldn't be trying to find electrical faults.

    You're going to need to get a qualified electrician in. Poking around inside an old 3-phase DB isn't something an untrained person should be doing, it's likely going to end in tears. Either the circuit is incorrectly wired in the DB or the geyser has an insulation fault or maybe even both. Specialised testers are needed to find the fault.
    _______________________________________________

    _______________________________________________

  7. Thanks given for this post:

    AmithS (02-Feb-21)

  8. #5
    New Member
    Join Date
    Jun 2012
    Location
    Vereeniging
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Greetings.I fully agree with this statement.Live and neutral both from the outgoing side of the earth leakage.
    Another problem I`ve found is that the geyser element is worn and so water seepage goes inside the element thus creating a leakage to earth.(Finding the slight tingling of electricity when touching the taps in the kitchen or bathroom.)This is more so applicable to old elements/geysers!This is just info people may use.

Similar Threads

  1. Earth Leakage Breaker (RCD) Tripping
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 14-Jul-23, 02:53 PM
  2. Ceiling fan tripping earth leakage.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 04-Feb-21, 09:04 AM
  3. earth leakage tripping issue
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 16-Jan-19, 12:13 PM
  4. [Question] If my geyser is tripping the earth leakage do I speak to a sparky or plumber
    By FEB in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 15-Jun-16, 08:46 AM
  5. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •