    Earth and neutral bridged in the prepaid meter which is usually in close proximity to the DB. Whole of East London. We have an ideal situation.

    Peace out ... Derek.

  2. #22
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Derlyn View Post
    Earth and neutral bridged in the prepaid meter which is usually in close proximity to the DB. Whole of East London. We have an ideal situation.

    Peace out ... Derek.
    So you use a TN-C-S system earthing ?

    We use a TN-C system earthing.
    Comments are based on opinion...not always facts....that's why people use an alias.

  3. #23
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    " Only some of the suburbs, especially the older one's, where the service cables are overhead, no earth is supplied. Only 2 wires. Live and neutral.

    My house, for instance, is in one of these older areas but being a newish house compared to the rest, has an underground service cable where a seperate earth is supplied.

    My test video will be uploaded this coming weekend.

    Peace out ... Derek"

    I need to read all the posts
    Comments are based on opinion...not always facts....that's why people use an alias.

  4. #24
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,483
    Thanks
    104
    Thanked 141 Times in 134 Posts
    Even where a seperate earth is supplied, it is still bridged with the neutral in the prepaid meter. Mine included.

    Supply Authority will NOT install the prepaid meter if that special copper link that is supplied with the meter bases is not in place between the earth and neutral on the meter base.

    Peace out ... Derek.

    Click image for larger version. 

Name:	Photo-0035.jpg 
Views:	159 
Size:	32.6 KB 
ID:	7998

    You will notice that even although there is an incoming earth, if you look closely you will see a bare copper bridge between the earth and neutral.

    That's how it's done here.
    Last edited by Derlyn; 21-Oct-20 at 09:07 AM.

  5. #25
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Your loop impedance test results must be low?

    I have been thinking ... this might not be a bad idea considering the rate at which earth wires are being removed from the overhead lines around here ... creating a huge problem with loop impedance tests.
    Comments are based on opinion...not always facts....that's why people use an alias.

  6. #26
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Derlyn View Post
    Even where a seperate earth is supplied, it is still bridged with the neutral in the prepaid meter. Mine included.

    Supply Authority will NOT install the prepaid meter if that special copper link that is supplied with the meter bases is not in place between the earth and neutral on the meter base.

    Peace out ... Derek.

    Click image for larger version. 

Name:	Photo-0035.jpg 
Views:	159 
Size:	32.6 KB 
ID:	7998

    You will notice that even although there is an incoming earth, if you look closely you will see a bare copper bridge between the earth and neutral.

    That's how it's done here.
    You should fit a main switch and a few cicuit breakers in your DB
    Comments are based on opinion...not always facts....that's why people use an alias.

  7. #27
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,483
    Thanks
    104
    Thanked 141 Times in 134 Posts
    Quote Originally Posted by ians View Post
    Your loop impedance test results must be low?
    Ian, my brother. Anything above 0,5 Ohms and we know there's something not right. I mean we only checking the earth loop impedance up to the meter.

    Fortunately we have a good relationship with the guys at Revenue in the Municipality.
    Take a photo of the sealed meter, make a call and request permission to break seals and pull the meter in order to carry out inspection on base.
    Inspection done, one call and a technician from Revenue is there within the hour to re seal.

    My brother, that is one department that's on the ball here in our valley.

    Peace out .. Derek.

Page 3 of 3 FirstFirst 123

Similar Threads

  1. Earth Leakage Breaker (RCD) Tripping
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 14-Jul-23, 02:53 PM
  2. Ceiling fan tripping earth leakage.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 04-Feb-21, 09:04 AM
  3. Low earth leakage tripping current
    By SeanM in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 15-Mar-19, 07:19 PM
  4. earth leakage tripping issue
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 16-Jan-19, 12:13 PM
  5. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12