    Earth leakage tripping with no load ?

    Hi all

    Just a little video as promised ( a man of my word ) made on 4th Feb 2020 showing that an earth leakage relay does not trip on a neutral earth fault without a load connected.

    Please forgive the filming quality. I am an electrician and not a film maker.

    https://www.youtube.com/watch?v=jxG3KFppbZc


    Peace out .. Derek.

  2. Thanks given for this post:

    ians (17-Oct-20)

  3. #2
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts
    Er. And?

  4. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,519
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Quote Originally Posted by skatingsparks View Post
    Er. And?
    I made this video in response to a number of active forum users who were / are under the impression that all earth leakage relays will trip on an earth to neutral fault even with no load connected. Not so.

    Peace out .. Derek

  5. #4
    Full Member
    Join Date
    Nov 2019
    Location
    Sa
    Posts
    32
    Thanks
    6
    Thanked 2 Times in 2 Posts
    Help me if I'm wrong guys but dis is not a problem because there will be no current on the neutral wire and when a second appliances(load) is connected it will cause the RCD to trip.

  6. #5
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,519
    Thanks
    106
    Thanked 146 Times in 139 Posts
    Quote Originally Posted by Frans400 View Post
    Help me if I'm wrong guys but dis is not a problem because there will be no current on the neutral wire and when a second appliances(load) is connected it will cause the RCD to trip.
    Exactly.

    Peace out .. Derek

  7. #6
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Chint is making arrangements to drop off a demo unit to test in my workshop ... lets see what happens.
    Comments are based on opinion...not always facts....that's why people use an alias.

  8. #7
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    " Only some of the suburbs, especially the older one's, where the service cables are overhead, no earth is supplied. Only 2 wires. Live and neutral.

    My house, for instance, is in one of these older areas but being a newish house compared to the rest, has an underground service cable where a seperate earth is supplied.

    My test video will be uploaded this coming weekend.

    Peace out ... Derek"

    I need to read all the posts
    Comments are based on opinion...not always facts....that's why people use an alias.

  9. #8
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I am curious to figue out why my earth leakage unit trips when I perform a similar test ...but Dereks unit doesnt.

    I need to figue how a 14 mA leakage current is displayed on the leakge current tester prior to it tripping without a load connected ... in fact both the test earth leakage and the unit in my sub DB trips shortly after the test bench unit trips ... i am going to bypass my Sub DB earth leakage unit

    John Ward explains in in a really simple manner ... as i have mentioned ... I understand that a leakage current of around 20-30mA or an unbalance between the live and neutral is required to trip the unit ... but what i dont understand is why my unit trips on the work bench ... what is creating the 14 mA displayed on my leakage current tester ... if no load is connected (ideal situation).

    in 99.9 % of the cases where the earth leakage has tripped when i touch the neutral ... the earht leakage has always been connected in a DB ... never a test bench situation ... when i carried out the test on my workbench I was hoping it wouldnt trip ... the only difference betwee nmy test and Derecks test ... I didnt use a plug and plug top ... i just touched a piece of wire between earth and neutral.



    https://www.youtube.com/watch?v=JTku...annel=JohnWard
    Comments are based on opinion...not always facts....that's why people use an alias.

  10. #9
    Junior Member
    Join Date
    Jun 2020
    Location
    Jhb
    Posts
    14
    Thanks
    0
    Thanked 6 Times in 4 Posts
    Quote Originally Posted by ians View Post
    I am curious to figue out why my earth leakage unit trips when I perform a similar test ...but Dereks unit doesnt.

    I need to figue how a 14 mA leakage current is displayed on the leakge current tester prior to it tripping without a load connected ... in fact both the test earth leakage and the unit in my sub DB trips shortly after the test bench unit trips ... i am going to bypass my Sub DB earth leakage unit

    John Ward explains in in a really simple manner ... as i have mentioned ... I understand that a leakage current of around 20-30mA or an unbalance between the live and neutral is required to trip the unit ... but what i dont understand is why my unit trips on the work bench ... what is creating the 14 mA displayed on my leakage current tester ... if no load is connected (ideal situation).

    in 99.9 % of the cases where the earth leakage has tripped when i touch the neutral ... the earht leakage has always been connected in a DB ... never a test bench situation ... when i carried out the test on my workbench I was hoping it wouldnt trip ... the only difference betwee nmy test and Derecks test ... I didnt use a plug and plug top ... i just touched a piece of wire between earth and neutral.



    https://www.youtube.com/watch?v=JTku...annel=JohnWard
    Hi Ian

    I haven't looked at the video, but thinking about a possibility:

    In an electrical circuit with a solid grounded neutral or star point the earth and neutral must be at the same potential. The voltage / potential difference between a live and neutral conductor must be exactly the same a the voltage measured between a live and ground conductor. And the voltage measured between neutral and earth should be 0 V.

    But in practical circumstances this is not always the case. So if the voltage difference between Neatral and Earth is sufficient to allow the Earth Leakage to detect a current flow of its rated current it will trip when you connect the earth and neutral down stream of the Earth Leakage device without any current flowing in the live conductor / or have a load connected.

  11. #10
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,487
    Thanks
    137
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Quote Originally Posted by ians View Post
    I am curious to figue out why my earth leakage unit trips when I perform a similar test ...but Dereks unit doesnt.

    I need to figue how a 14 mA leakage current is displayed on the leakge current tester prior to it tripping without a load connected ... in fact both the test earth leakage and the unit in my sub DB trips shortly after the test bench unit trips ... i am going to bypass my Sub DB earth leakage unit

    John Ward explains in in a really simple manner ... as i have mentioned ... I understand that a leakage current of around 20-30mA or an unbalance between the live and neutral is required to trip the unit ... but what i dont understand is why my unit trips on the work bench ... what is creating the 14 mA displayed on my leakage current tester ... if no load is connected (ideal situation).

    in 99.9 % of the cases where the earth leakage has tripped when i touch the neutral ... the earht leakage has always been connected in a DB ... never a test bench situation ... when i carried out the test on my workbench I was hoping it wouldnt trip ... the only difference betwee nmy test and Derecks test ... I didnt use a plug and plug top ... i just touched a piece of wire between earth and neutral.
    I suspect that you have a potential difference between Neutral and Earth on your incoming side, which causes a current to flow from the Neutral to Earth through the ELU when you short them out. It sees this imbalance of current and trips.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

Page 1 of 3 123 LastLast

Similar Threads

  1. Earth Leakage Breaker (RCD) Tripping
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 14-Jul-23, 02:53 PM
  2. Ceiling fan tripping earth leakage.
    By Derlyn in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 04-Feb-21, 09:04 AM
  3. Low earth leakage tripping current
    By SeanM in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 15-Mar-19, 07:19 PM
  4. earth leakage tripping issue
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 16-Jan-19, 12:13 PM
  5. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12