    Quote Originally Posted by Trevor Varner View Post
    Could someone please show me where round boxes are not allowed to have terminations done in them, I can understand joints not allowed in T pieces etc.
    I would love some clarity on that too.

    Quote Originally Posted by Derlyn View Post
    On the right is a connection box that is not weatherproof and is ideal for downlights. It's called a RIP BOX available from ARB for R29.
    It's great to see that the RIP Box has come down to a far more competitive price from when it was first launched.

  2. #42
    Full Member
    Join Date
    Aug 2009
    Location
    Newcastle
    Posts
    33
    Thanks
    0
    Thanked 3 Times in 3 Posts
    Derlyn it started out as connection to down lighters but the rest is not really wondering of the point as it is about how we make connections to be safe. Back to the point of the round box. Yes most light fittings have a connector on them. But what if its one of those lights that just have the piece of flex with the holder on the end ? Also what do you do if you have more than 1 neutral as most holders cant take 2 as they are barely big enough for one ? Not being funny but using a round box to make connections in then to me seems perfectly fine as it ticks all the boxes. The cables are secured ( if you use glands )no live conductors can be touched with the standard test finger with out removing a cover with a tool ( thats if you put on a cover) and can be serviced if it is in a place where you can reach it and you use block connectors to join the cables. To make it maintenance free if it is in a place where it cant be reached use ferrules and heat shrink. I would personally not just twist the wires together and tape them or use a screwit. I have seen more screwits come loose with out much effort than I have seen correctly selected block connectors melt. Correct me if I am wrong but I have seen joints in round boxes in houses with black metal tubing,black plastic tubing,white plastic tubing. The little round box has been there long before any of the other fancy junction boxes we have today has come on the market and I think thats why it has been used for joining cables for as long as most electricians can remember. The are also to me much sturdier and hold the cables beter. I will even admit that I have used them a few times to even make joints thats buried under the ground. I stuffed them full of that black putty compound. I know of at least one thats probably 18 years old and still in the ground and they are still working away with no problems.


    Sent from my iPhone using Tapatalk

  3. #43
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,790
    Thanks
    557
    Thanked 909 Times in 734 Posts
    Quote Originally Posted by Dave A View Post
    Am I ever in for an interesting discussion with my electricians tomorrow morning...
    How did the toolbox talk go?
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  4. #44
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,023
    Thanks
    3,178
    Thanked 2,581 Times in 2,177 Posts
    Blog Entries
    12
    Quote Originally Posted by AndyD View Post
    How did the toolbox talk go?
    In this age of masks, I couldn't see what the mouths were doing. But all eyes went as big as saucers. Feedback is when it comes to Durban, there are connections in round boxes virtually everywhere we go...

  5. #45
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    2,507
    Thanks
    116
    Thanked 206 Times in 180 Posts
    Quote Originally Posted by Dave A View Post
    In this age of masks, I couldn't see what the mouths were doing. But all eyes went as big as saucers. Feedback is when it comes to Durban, there are connections in round boxes virtually everywhere we go...
    no surprise

    Personally i have never come across a building in Durban where round conduit boxes are not being used as connection/junction boxes for lights ... 5 amp socket outlets ... dome lids with extractor fans ... you name it ... it is being used as a junction box for terminating cables

    In fact while collecting equipment at AC/DC ... all the wago demo units display are using round conduit boxes as junction boxes.
    Comments are based on opinion...not always facts....that's why people use an alias.

  6. #46
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,790
    Thanks
    557
    Thanked 909 Times in 734 Posts
    Quote Originally Posted by Dave A View Post
    In this age of masks, I couldn't see what the mouths were doing. But all eyes went as big as saucers. Feedback is when it comes to Durban, there are connections in round boxes virtually everywhere we go...
    Yeah, it's standard practice everywhere I've been in SA. Given the regs defer to the manufacturers instructions, if a round box wasn't marked specifically to forbid internal connections and there wasn't a manufacturers spec sheet available on site would you fail the installation for a CoC?
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  7. #47
    Full Member
    Join Date
    Aug 2009
    Location
    Newcastle
    Posts
    33
    Thanks
    0
    Thanked 3 Times in 3 Posts
    Originally from Cape town and I can tell you its as common as anything. Also here in Bloemfontein where I am currently.

Page 5 of 5 FirstFirst ... 345

Similar Threads

  1. Using 72mm pipe as downlight boxes
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 13-Jun-19, 04:17 AM
  2. [Question] Air Conditioner connections
    By SeanM in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 14-Feb-19, 02:56 PM
  3. 12v Downlight to 230vac conversions.
    By hartdev@hotmail.com in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 13-Sep-15, 07:59 AM
  4. 220v Downlight DIY Installation
    By daveob in forum Electrical Contracting Industry Forum
    Replies: 42
    Last Post: 24-Jan-13, 07:21 AM
  5. Municipal Connections
    By Alan in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 01-Jun-06, 10:47 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •