    Question Are lead gel battery's bank legal in a residential power back up system?

    Most of the inverter power back up system I see uses lead acid or gel battery's instead of lithium-iron phosphate battery's. According to me if lead battery's can emit explosive gasses that will cause the installation to be classified as a hazardous location.

    Am I allowed to install a 600ah 48v battery bank in a garage ?
    And if it's legal should it be CoC by a master installation electrician ?

  2. #2
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Frans400 View Post
    Most of the inverter power back up system I see uses lead acid or gel battery's instead of lithium-iron phosphate battery's. According to me if lead battery's can emit explosive gasses that will cause the installation to be classified as a hazardous location.

    Am I allowed to install a 600ah 48v battery bank in a garage ?
    And if it's legal should it be CoC by a master installation electrician ?
    You need to understand how an area is classified ... the location ... the size of the room ... volume of gas ... the air flow .. when the flamable gas ispresent ... etc etc.
    Comments are based on opinion...not always facts....that's why people use an alias.

  3. #3
    Full Member
    Join Date
    Nov 2019
    Location
    Sa
    Posts
    32
    Thanks
    6
    Thanked 2 Times in 2 Posts
    excerpt from sans 10142-2017
    7.14 Hazardous locations
    7.14.1 The class of a hazardous location shall be determined before the
    installation is designed. The classification of hazardous locations for the
    purpose of electrical installation work shall be carried out by a person who is
    competent to express an opinion on such locations. The appropriate
    electrical equipment shall be installed in accordance with a standard adopted
    by the appropriate statutory authority.


    So what will make me a competent person? should I study sans 10108 only or do I need to become a master installation electrician?

  4. #4
    Junior Member
    Join Date
    Jun 2020
    Location
    Jhb
    Posts
    14
    Thanks
    0
    Thanked 6 Times in 4 Posts
    Quote Originally Posted by Frans400 View Post
    Most of the inverter power back up system I see uses lead acid or gel battery's instead of lithium-iron phosphate battery's. According to me if lead battery's can emit explosive gasses that will cause the installation to be classified as a hazardous location.

    Am I allowed to install a 600ah 48v battery bank in a garage ?
    And if it's legal should it be CoC by a master installation electrician ?


    Hi Frans

    Your typical household installation will consist of 4 to maybe 8 batteries, usually of the valve-regulated type. During charging the amount of hydrogen released from these banks within a large space like a double garage will be below the explosive concentration limits.

    In your case with what looks like 24 batteries I would perform the calculation as per SANS 10108:2014 “The Classification of hazardous locations and the selection of equipment for use in such locations”

    Here is nice guide:

    https://mtexlab.co.za/uploads/6/3/7/...2016_rev_2.pdf

    These calculations are performed by a MIE

  5. Thank given for this post:

    AndyD (02-Oct-20), Frans400 (30-Sep-20), ians (04-Oct-20)

  6. #5
    Full Member
    Join Date
    Nov 2019
    Location
    Sa
    Posts
    32
    Thanks
    6
    Thanked 2 Times in 2 Posts
    Hi

    Please help me if I'm incorrect.

    So depending on the charge current and the amount of lead acid(or gel)cells in the configuration the installation will be classified as an zone 1 or 2 hazardous location?

    But because zone 1 is seen as a hazardous location (even though its falls below the criteria to create a explosive atmosphere) the installation should be CoC'ed by a MIE?

Similar Threads

  1. max Uoc allowed on residential off grid (non embedded) system
    By Frans400 in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 25-Sep-20, 08:04 AM
  2. ELU turns off after power goes back on
    By ELECT 1 in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 04-Apr-20, 08:40 AM
  3. [Question] Power of attorney for personal bank account arrangements
    By leuce in forum Business Finance Forum
    Replies: 3
    Last Post: 22-Nov-11, 02:52 PM
  4. New demerit system-New driving points system hits the road
    By Candy Bouwer in forum General Business Forum
    Replies: 22
    Last Post: 23-Jul-09, 06:51 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •