    Stove on E/L

    Sorry if this is a silly question but my work is 90% commercial and industrial but we have got a big dommestic (block of flats) to bring to standard.

    Stoves/oven - I have never seen a stove coupler in my electrical life in the 12 years I have been here . I also never seen, unless main switch on the DB is an Earth Leakage or the stove/oven plugs in to a socket, a cooking appliance covered by earth leakage - just a double pole isolator by the side of the appliance.

    I saw on the back of some of the (admittedly mostly quite old) stoves that there was a lable stating "Must not be connected via Earth Leakage".

    I also saw some flats had cut the plug off and connected to an (very old) existing 6mm cable - obviously not right.

    What must we give people to connect there stoves? Where does my responsibility end?
    In most cases I have seen just a double pole isolator supplied by a 6mm not on earth leakage.
    What control do we have over the next tennant coming in connecting up to the cut of 6mm the last tennat left?

    My take is if a stove is under 16amps then connect via earth leakage plug to and that fine.

    But in these flats they are mostly big stoves and most are 6mm cables (in various states from the old cloth covered cable to new twin and earth) on 32 amp breakers going to double pole islators and then a 6mm down to where its connected to the stove.

    I know these stoves will cause nuisance tripping of on earth leaklage and, honestly, I don't want to be forever being called back because the tennants crapped out (and most of them are crappy old things) but if the rule is - must be on earth leakage then thats what I'll do.

    Am I misreading part of the SANS 10142?

    Only asking as like I said - never seen a stove coupler - never seen stove on the Earth leakage side of the board. Its usually in there next to the lighting breakers.

    Advice please. Asking because I want to do it right before the keyboard warriors slate me.

  2. #2
    Silver Member
    Join Date
    Mar 2008
    Posts
    244
    Thanks
    4
    Thanked 44 Times in 37 Posts

    No worries - I got it

    So from what I understand - a free standing stove is via Stove coupler or must be on earth leakage. If fixed standard double pole is fine.

  3. #3
    Silver Member
    Join Date
    Mar 2008
    Posts
    244
    Thanks
    4
    Thanked 44 Times in 37 Posts
    Next question - where on earth do I get them from? In Germiston, Guateng.

  4. #4
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    2,886
    Thanks
    105
    Thanked 585 Times in 496 Posts
    Blog Entries
    1
    Maybe these guys, note I have never used them before so can not vouch for them.

    Union Electrical
    Contact Details
    Tel(011) 873-4060
    Fax(011) 873-8376


    Physical Address
    Corner President & Kinross Streets,
    Germiston,
    1401
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar and LED lighting solutions - www.microsolve.co.za

  5. #5
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    21,978
    Thanks
    3,171
    Thanked 2,571 Times in 2,168 Posts
    Blog Entries
    12
    Quote Originally Posted by skatingsparks View Post
    So from what I understand - a free standing stove is via Stove coupler or must be on earth leakage. If fixed standard double pole is fine.
    Not quite that simple. That is for stoves rated over 16A....
    Below 16A and the free-standing stove can be hard wired in and off earth leakage (provided there is not an isolator/socket outlet "combo" on the circuit).

    I know it's not officially published yet, but the draft of edition 3 is out and about (and this amendment on stove connections isn't about to change). It is going to be a requirement (per edition 3) that the tails after the stove isolator can't be left in place when the stove is disconnected.

    So to answer your question about responsibility and CYA:
    1. Remove the tails if the free-standing stove isn't there / connected.
    2. Take photos.

  6. #6
    Platinum Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    2,389
    Thanks
    107
    Thanked 199 Times in 173 Posts
    Quote Originally Posted by Dave A View Post
    Not quite that simple. That is for stoves rated over 16A....
    Below 16A and the free-standing stove can be hard wired in and off earth leakage (provided there is not an isolator/socket outlet "combo" on the circuit).

    I know it's not officially published yet, but the draft of edition 3 is out and about (and this amendment on stove connections isn't about to change). It is going to be a requirement (per edition 3) that the tails after the stove isolator can't be left in place when the stove is disconnected.

    So to answer your question about responsibility and CYA:
    1. Remove the tails if the free-standing stove isn't there / connected.
    2. Take photos.
    After attending an investigation 20 + years ago in Westville where a 2 year old child was electrocuted to death ... the previous owner disconnected and removed the stove and left the tails on the foor ... new owners were moving in not aware that the wires were live.

    Rule or no rule you NEVER EVER EVER leave the tails after disconnecting the stove ... remove the tails and leave them in the cupboard.

    I dont believe a stove should be on earth leakage ... I have had too many nuisance trips ...even after replacing a new element ... if there is one of those old plug stove isolator combos ... i remove the combo ... fit a plate to cover the big hole (you can buy them from the electrical wholsaler) and fit an isolator and make sure the stove is connected properly with lugs and not wires twisted around the bolts.
    Comments are based on opinion...not always facts....that's why people use an alias.

  7. #7
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    21,978
    Thanks
    3,171
    Thanked 2,571 Times in 2,168 Posts
    Blog Entries
    12
    Quote Originally Posted by Dave A View Post
    Not quite that simple. That is for stoves rated over 16A....
    Below 16A and the free-standing stove can be hard wired in and off earth leakage (provided there is not an isolator/socket outlet "combo" on the circuit).
    Seems I have got this wrong (My apologies). Currently all free-standing stoves need to be on a stove coupler or socket outlet...

    But this may be changing with edition 3.

  8. #8
    Silver Member
    Join Date
    Mar 2008
    Posts
    244
    Thanks
    4
    Thanked 44 Times in 37 Posts
    Spoke to every wholesaler in a very big radius - 99% have never seen or heard of stove couplers.
    Phoned ECA - free standing stove, if not connected to stove coupler, must be via appropriate plug (industrial 32 amp in my case) covered by earth leakage.
    Currently I connected direct to stove - 32 breaker covered by earth leakage through double pole isolator then stove. Now I'm going to add the socket.
    It's already causing problems with nuisance tripping.
    Customer points out on the stove there is label saying not to connect to earth leakage as can cause nuisance tripping. Checked the manuals (that I can find) for the stoves and the ones I found state - no need for earth leakage.

    Do I go to SANS 10142 or does manufacturers instruction over rule the need for E/Leakage - I mean it's written on most of the stoves I have seen.

    If there was no stove I installed as above and enclosed the cable in a conduit box in 60amp connectors.

  9. #9
    Silver Member
    Join Date
    Mar 2008
    Posts
    244
    Thanks
    4
    Thanked 44 Times in 37 Posts
    Obviously advised client to not use stove until they carry out repair causing nuisance tripping.

Similar Threads

  1. Stove Connection
    By Ishmaelmo in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 04-May-19, 01:41 PM
  2. COC for an electric stove
    By ians in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 06-Sep-18, 08:29 PM
  3. gas stove connection
    By ians in forum General Chat Forum
    Replies: 3
    Last Post: 09-Feb-15, 11:44 AM
  4. COC for a gas stove
    By ians in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 23-Jan-15, 01:24 AM
  5. stove plate
    By murdock in forum Technology Forum
    Replies: 7
    Last Post: 31-Mar-10, 11:24 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •