    COC's on Solar PV and DC installations

    How do you go about doing a COC on a solar system with 8KW inverter and a couple batteries? My understanding is that it would be 3 seperate testes done on each of this sections such as the voltages, and Earth Fault Loop Impedance, what else needs to be tested on the solar panel side? Inverter side?, Battery side and Grid side? on p263 it talks about the Prospective short circuit current test on DC, What is meant by "total resistance of the upstream network"? it also says you can use the PSCC that the manufacturer used at the terminals (8.4.6.4) would you write down the manufacturer's rating on 1 battery or add up all the batteries and use that as the PSCC?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,248
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    There was a previous thread on PV and DC which will provide some pointers

    https://www.theforumsa.co.za/forums/...+Installations

    PSCC on batteries would be for the bank - Rule of thumb is 12 x Amp hour rating of battery bank -Don't trust me on that. There is a calculation that you can do and it is found in SANS10142-1 ED2 Clause 8.4.6.3
    There is also a draft document out for public comment on PV systems and the tests required that may be useful
    There was a previous thread on PSCC and I have put the link further down

    8.4.6.3 The prospective short-circuit current of batteries in ampere (A) can
    be calculated using the following formula:
    PSCC =Eb/Rbbr

    where
    EB is the open-circuit voltage of the batteries; if this information
    is not known, then use
    EB = 1,05 x UNB V (where UNB = 2,0 V/cell);
    RBBr is the total resistance of the upstream network, in ohms (Ω),
    including the internal resistance of the battery and the
    resistance of the conductors;
    RBBr = 0,9 x RB + RBL + Ry Ω (see figure 8.1);
    RB is the internal resistance of the battery;
    RBL is the resistance of the battery connections;
    Ry is the resistance of the conductors.
    NOTE The internal resistance of the battery can be obtained from the manufacturer's
    data.
    Figure 8.1 — Resistance components in a battery power source circuit
    8.4.6.4 Alternatively the estimated PSCC at the battery terminals, as
    supplied by the manufacturer of the battery, may be used.


    https://www.theforumsa.co.za/forums/...highlight=PSCC

Similar Threads

  1. COC for PV Solar installations
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 30-May-20, 10:02 AM
  2. Solar system installations
    By Siya Saver in forum Energy and Resource Conservation Forum
    Replies: 7
    Last Post: 10-Dec-18, 09:26 AM
  3. Solar installations
    By DieterT in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 21-Apr-15, 07:52 AM
  4. Stand alone Solar/Pv installations
    By CollenD in forum Electrical Contracting Industry Forum
    Replies: 19
    Last Post: 13-Jun-12, 02:21 PM
  5. CoC requirements for Solar Water Heating installations
    By Carbonic in forum Electrical Contracting Industry Forum
    Replies: 15
    Last Post: 07-Sep-10, 08:59 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •